Something odd happened last night.  The wife was awakened by what she called a "sizzling" sound coming from the bathroom.  Woke me up and I found this:



Disregard the test outlet I wired in right before this pic.

Notice that the hot wire got really hot and melted its insulation and fried the GFI box.  

The hot side of the GFI box is burned.  

What caused this and how do I repair such a short wire?

Link Posted: 8/25/2016 8:06:41 PM EDT
[#1]
Loose connection caused arc probably.

What kind of load were you drawing on it?
Link Posted: 8/25/2016 8:13:10 PM EDT
[#2]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Loose connection caused arc probably.

What kind of load were you drawing on it?
View Quote


There was an iphone charger plugged into it. They have this circuit wired to the garage and there was a fridge plugged in out there.  Been here 11 years and nothing out of the ordinary.

Link Posted: 8/25/2016 8:15:23 PM EDT
[#3]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


There was an iphone charger plugged into it. They have this circuit wired to the garage and there was a fridge plugged in out there.  Been here 11 years and nothing out of the ordinary.

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Loose connection caused arc probably.

What kind of load were you drawing on it?


There was an iphone charger plugged into it. They have this circuit wired to the garage and there was a fridge plugged in out there.  Been here 11 years and nothing out of the ordinary.



Did the phone charger short out?
Link Posted: 8/25/2016 8:17:18 PM EDT
[#4]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Loose connection caused arc probably.

What kind of load were you drawing on it?
View Quote

Most likely. High resistance (loose) connection = heat.

ETA, from now on, land the wires on the screw terminals, don't shove them into those crappy stabbing slots.
Link Posted: 8/25/2016 8:18:19 PM EDT
[#5]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Did the phone charger short out?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Loose connection caused arc probably.

What kind of load were you drawing on it?


There was an iphone charger plugged into it. They have this circuit wired to the garage and there was a fridge plugged in out there.  Been here 11 years and nothing out of the ordinary.



Did the phone charger short out?


Don't know.  It still works.  It happened about 2am.  
Link Posted: 8/25/2016 8:19:58 PM EDT
[#6]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Don't know.  It still works.  It happened about 2am.  
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Quoted:
Loose connection caused arc probably.

What kind of load were you drawing on it?


There was an iphone charger plugged into it. They have this circuit wired to the garage and there was a fridge plugged in out there.  Been here 11 years and nothing out of the ordinary.



Did the phone charger short out?


Don't know.  It still works.  It happened about 2am.  


Probably just a loose connection. I'd rewire it right and keep an eye on it.
Maybe replace the breaker too.
Link Posted: 8/25/2016 8:20:29 PM EDT
[#7]
Backstabbing sucks. Make the proper connections when you replace the
Link Posted: 8/25/2016 8:23:16 PM EDT
[#8]
The black wire is naked to inside the box.  What do I do about the burnt insulation?
Link Posted: 8/25/2016 8:24:28 PM EDT
[#9]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?
View Quote

Hopefully you can pull some slack, but I doubt it.
Link Posted: 8/25/2016 8:26:06 PM EDT
[#10]
Link Posted: 8/25/2016 8:28:29 PM EDT
[#11]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?
View Quote


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.

Link Posted: 8/25/2016 8:29:08 PM EDT
[#12]



This would be a great time to call an actual Electrician ! ! !


Link Posted: 8/25/2016 8:32:19 PM EDT
[#13]
Discussion ForumsJump to Quoted PostQuote History
Quoted:



This would be a great time to call an actual Electrician ! ! !


View Quote



Lol!  

No need for that
Link Posted: 8/25/2016 8:33:36 PM EDT
[#14]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.



I pulled a little.  Didn't seem to have any slack.
Link Posted: 8/25/2016 8:36:04 PM EDT
[#15]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


I pulled a little.  Didn't seem to have any slack.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.



I pulled a little.  Didn't seem to have any slack.

Hard to tell from the pic, but is there a strain relief where the wires come in the box that could be loosened?
Link Posted: 8/25/2016 8:36:37 PM EDT
[#16]
I want to know how you had two devices (GFCI, and duplex) fit into one single gang box.
Link Posted: 8/25/2016 8:43:01 PM EDT
[#17]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


I pulled a little.  Didn't seem to have any slack.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.



I pulled a little.  Didn't seem to have any slack.


How good are you at sheet rock repair?
Link Posted: 8/25/2016 8:43:07 PM EDT
[#18]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
I want to know how you had two devices (GFCI, and duplex) fit into one single gang box.
View Quote


I think he was using the second outlet for testing purposes.
Link Posted: 8/25/2016 8:43:13 PM EDT
[#19]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
I want to know how you had two devices (GFCI, and duplex) fit into one single gang box.
View Quote


RIF



















Link Posted: 8/25/2016 8:43:37 PM EDT
[#20]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


How good are you at sheet rock repair?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Quoted:
The black wire is naked to inside the box.  What do I do about the burnt insulation?


Didn't see that. Like stated you need to pull enough good wire out of the wall or you will have to run a new wire.



I pulled a little.  Didn't seem to have any slack.


How good are you at sheet rock repair?


That's the $500 question
Link Posted: 8/25/2016 8:45:19 PM EDT
[#21]
Don't backstab the new one.
Link Posted: 8/25/2016 8:46:14 PM EDT
[#22]
Is the stud to the left or the right of that box?  You might be in luck if it's to the left.

Link Posted: 8/25/2016 8:55:45 PM EDT
[#23]

Discussion ForumsJump to Quoted PostQuote History
Quoted:





View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:

Backstabbing sucks.


That is an internal screw clamp. No gfcis were "back stabbed". Ever.
Link Posted: 8/25/2016 8:57:10 PM EDT
[#24]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Is the stud to the left or the right of that box?  You might be in luck if it's to the left.
View Quote


Stud is on the right  

Wire is tight.  I can go under tomorrow and see if I can find an inch to push up. August in a crawlspace.  I hate spiders  
Link Posted: 8/25/2016 8:59:55 PM EDT
[#25]
Quoted:


The hot side of the GFI box is burned.  

What caused this and how do I repair such a short wire?

View Quote


Some GFIs are junk and burn up. I have replaced about 6 from it. 4 of them were internal failures. 2 melted from the outside in.
Link Posted: 8/25/2016 9:00:21 PM EDT
[#26]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Stud is on the right  

Wire is tight.  I can go under tomorrow and see if I can find an inch to push up. August in a crawlspace.  I hate spiders  
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Is the stud to the left or the right of that box?  You might be in luck if it's to the left.


Stud is on the right  

Wire is tight.  I can go under tomorrow and see if I can find an inch to push up. August in a crawlspace.  I hate spiders  


Kill the whole thing with fire!
Link Posted: 8/25/2016 9:01:04 PM EDT
[#27]
What caused it?





11 years of refrigerator load on a 15 amp gfci.







Unless you are willing to run a dedicated circuit to the fridge (which it should be any ways), your best bet is this...







Get rid of that line and load bullshit. There is NO REASON to have a plug in your bathroom controlling the garage. They wired shit that way 30 yrs ago. These days, your garage is generally it's own circuit.







Connect all the whites and put a 6" pigtail on it, do the same with the blacks. Install a new TAMPER proof gfci receptacle.







Go out to the garage, and remove the outlet by the fridge and replace with NEW gfci receptacle.







Be sure to turn off the breaker. Lol.







 


 
Link Posted: 8/25/2016 9:02:55 PM EDT
[#28]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Some GFIs are junk and burn up. I have replaced about 6 from it. 4 of them were internal failures. 2 melted from the outside in.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:


The hot side of the GFI box is burned.  

What caused this and how do I repair such a short wire?



Some GFIs are junk and burn up. I have replaced about 6 from it. 4 of them were internal failures. 2 melted from the outside in.


We have been here 11 years and it was already installed.  I have no idea how old it is.  

It tripped during the incident and I pushed the reset button with nothing plugged in and it smoked until it burned up but never tripped again.  Main breaker did not trip either
Link Posted: 8/25/2016 9:02:58 PM EDT
[#29]
How much clean wire can you get on that burned up hot?  If there is enough clean, undamaged wire to get a wire nut on- probably at least a couple inches- you can attach a 6 inch piece of the same size wire and make the situation work.
Link Posted: 8/25/2016 9:06:03 PM EDT
[#30]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
What caused it?

11 years of refrigerator load on a 15 amp gfci.


Unless you are willing to run a dedicated circuit to the fridge (which it should be any ways), your best bet is this...


Get rid of that line and load bullshit. There is NO REASON to have a plug in your bathroom controlling the garage. They wired shit that way 30 yrs ago. These days, your garage is generally it's own circuit.


Connect all the whites and put a 6" pigtail on it, do the same with the blacks. Install a new TAMPER proof gfci receptacle.


Go out to the garage, and remove the outlet by the fridge and replace with NEW gfci receptacle.


Be sure to turn off the breaker. Lol.


 
 
View Quote


Everything is finished and I hate to cut and repair 50' of sheetrock.  I plan to rewire the garage when I finish my addition but that involves burying 50' of wire to feed a subpanel.
Link Posted: 8/25/2016 9:07:07 PM EDT
[#31]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
How much clean wire can you get on that burned up hot?  If there is enough clean, undamaged wire to get a wire nut on- probably at least a couple inches- you can attach a 6 inch piece of the same size wire and make the situation work.
View Quote


This is what they did for the feeders going out but that box is getting full.
Link Posted: 8/25/2016 9:42:06 PM EDT
[#32]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


This is what they did for the feeders going out but that box is getting full.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
How much clean wire can you get on that burned up hot?  If there is enough clean, undamaged wire to get a wire nut on- probably at least a couple inches- you can attach a 6 inch piece of the same size wire and make the situation work.


This is what they did for the feeders going out but that box is getting full.


It's your only easy option and would be a safe repair..  Use stranded wire and you should be able to get another GFCI in there without too much trouble.  Just don't downsize it.
Link Posted: 8/26/2016 9:25:13 AM EDT
[#33]
Link Posted: 8/26/2016 9:27:16 AM EDT
[#34]
Gotta make those screws TIGHT.



Probably a loose connection and when your SO went to unplug or plug in her phone it moved the outlet just enough to arc.
Link Posted: 8/26/2016 9:34:08 AM EDT
[#35]
The easy fix would be to slide some heat shrink up past the insulation, then hit it with a hairdryer.
Then, as stated use the screws on a new plug. Was probably loose,to cause the meltdown. I HATE GFI plugs.
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top