Quick rundown.. 10 year old Lennox heat pump with elec aux. Since I purchased the house 5 years ago, I have practically rebuilt the system.
- Replaced 24v transformer - old one failed. Replaced with HD unit for industrial control
- Replaced 3A fuse with "Lil Popper" external breaker - great for when system is fucking up
- Replaced defrost control board on compressor - original board had cracked PCB
- Replaced compressor contactor - old contactor had eroded points
- Replaced condenser fan and air handler fan run capacitors - why not? They were 10 years old.
- Replaced reversing valve coil
- Had small leak in reversing valve assy. brazed, system evacuated, recharged, and pressure tested good
Before I replaced the reversing valve coil, the system would blow the 24v fuse about once a month. Usually would happen during the cold months when the system was cycling into defrost. When it did, it seemed like I was chasing a ghost to find the problem, which is why I installed the 3A 24v breaker. After replacing the coil, the issues seemed to go away. Later on during the summer, I discovered a small leak in the reversing valve assy, and had it eventually repaired after several HVAC outfits claimed that it could not be done - I just identified the leak location at a failed factory braze, and had a tech glob a bunch of silver solder onto it. He then evacuated the system, nitrogen purged it, recharged and tested it. It ran great through the summer and through the winter.
Just this morning I woke up and found that the 24v breaker was blown. Resetting it had no effect. Went outside and checked everything on the compressor, blew out some insect debris, and restarted everything. Breaker does not reset. Wait for compressor to kick in. It kicks in, and then almost immediately blows the 24v breaker again.
I tried disconnecting the reversing valve coil at the defrost control board, and reset the 24v breaker. It now stays on.
I did a resistance test on the reversing valve coil and got 15.8 ohms which seems to be within spec. I also set the system into cooling mode with the compressor shut down, and verified that the coil had good magnetic pull, which it did. I then reinstalled the coil, put the compressor back together, and energized the whole system. It started up and has been running normally for several hours now.
The only part of the defrost system that I have not replaced, is the temperature sensor on the compressor. The system has both demand and timed defrost. The timed defrost is set to 90min accumulated runtime since it never gets that cold here. The demand defrost sensor seems to work as the unit will go into defrost on its own if it begins to frost.
I'm just about to purchase a new reversing valve coil just in case, but I grow tired of throwing parts at the system. Anyone have an idea or stuff to check?