Link Posted: 3/21/2017 1:49:21 PM EDT
[#1]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
All breakers are suitable for on/off operation.

Breakers marked SWD or HID are suitable for regular, ie, thousands of cycles over their lifetime operation of the following:

SWD:
Fluorescent lighting

HID:
Fluorescent lighting
High Intensity Discharge lighting

These are the only breakers, and approved loads, for routine, high use off/on operations.  Anything else is best done on an as-needed basis or, for higher loads that will be regularly switched, done with a relay/contactor or other controller.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:

They are 20 amp SWD breakers, so they are suitable for on/off operation 
All breakers are suitable for on/off operation.

Breakers marked SWD or HID are suitable for regular, ie, thousands of cycles over their lifetime operation of the following:

SWD:
Fluorescent lighting

HID:
Fluorescent lighting
High Intensity Discharge lighting

These are the only breakers, and approved loads, for routine, high use off/on operations.  Anything else is best done on an as-needed basis or, for higher loads that will be regularly switched, done with a relay/contactor or other controller.
The last time I installed an A/C Condenser I used a Rheem.

Instead of a monster contactor with copper surfaces it had a small single pole high current relay with expensive contacts.

Worked like a charm.

There is no reason to open both legs of a 240 V compressor motor to turn it on and off.

There is a disconnect beside the unit for killing all the power when required (and it is out of sight of the panel supplying it).
Link Posted: 3/28/2017 4:28:30 PM EDT
[#2]
Didn't read the whole thread but I read that the house was built in 95.
In Canada since the late 70's all kitchen receptacles have to be individual circuits.
In other words every double counter plug is run with 14/3 wire which has a white black and red wire.
The neutral goes to the side with the silver screws.
On the opposite side which has gold screws you cut the jumper bar between the 2 screws and you place the black wire on one screw and the red wire on the other.
At the panel end the white goes to the neutral bar the red to one breaker and the black to another.
This way each plug has its own 15 A circuit.

Circuits are designed to run at 80% so a 15 A circuit should only be run at 12 A.
Remeber that Watts/Volts = Amps

14 Ga wire is good for a 15 A circuit.
12 Ga wire is good for a 20 A circuit.


ETA: If your house is properly wired and somebody added the dishwasher after the fact you can remove the double counter plug and replace it with a single counter plug and use the second circuit for the dishwasher.

NEVER RUN A 20 A BREAKER ON 14 GA WIRE UNLESS YOU ARE INDEPENDENTLY WEALTHY AND CAN AFFORD TO PAY FOR REBUILDING YOUR HOUSE AFTER A FIRE BECAUSE YOUR INSURANCE COMPANY WON'T COVER YOU.
Page / 2
Next Page Arrow Left
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top