Posted: 4/19/2017 4:38:45 PM EDT
Last year my AC froze up, I read it could be as a result of an airflow issue and sure enough, I had forgotten to change the filter. Swapped it out and no more issues.
Anyway, it froze up again yesterday, even though my filter is almost brand new, what could be causing this? |
|
|
|
+1 to the low on coolant responses. to thaw it out, just run it on fan for a few hours. that'll buy you some time before the a/c guy comes over. he can't troubleshoot/fix it if your coil is frozen over so might as well start thawing it.
|
|
When this happened last summer, they checked my coolant levels and they said they were ok, but it could be a blockage in the line somewhere. Cause once I thawed it out, it never came back all summer (struggled to keep up though, old system). I changed the attic and outside unit out back in Feb.
|
|
Quoted:
I only froze up once and then was fine all year, does that sound right? View Quote And ditto on thawing the coils before he gets there. |
|
|
Quoted:
I only froze up once and then was fine all year, does that sound right? View Quote We have 10 HVAC units in our office. |
|
Quoted:
If I had a leak, where would it be likely to be? Anywhere? View Quote |
|
Could be a lot of things. Cheapest easiest is air flow (filter).
Next thing I would check is the Evap coil itself being dirty, not allowing air to pass. Then superheat/subcool to check Refrigerant levels, txv (if applicable) operation, and for an over/under charge. Systems don't usually just start leaking out of the blue... Unless it's a shrader valve. Then look for non condensables in the system. Generally speaking, evap coil freezing up means the system is to cold, so it's not pulling enough air through it to evaporate the refrigerant. Or possibly incorrectly charged, (pressure/temperature relationship). It's hard to diagnose without the proper tools. Eta: YMMV, everyone has their own opinion/experience. |
|
Low coolant can cause it.
But it could still be an airflow issue. The coils may be heavily caked with dust/dirt causing condensation to build up around it and freeze into a dirt/ice block. Happens to several units a year on the apartment complex I manage. I would clean the coils first and see if this fixes it before calling the HVAC guys out. If your airflow seems low through the vents when it's not frozen this is likely the case. While it is frozen just switch the thermostat to fan, it will go from blowing no air to cool air to warm air once it is thawed. |
|
|
If the coolant levels are OK you could also have a restriction or piece of debris in the thermal expansion valve...meaning it acts like its low and freezes up when you get hot enough weather. I've had that happen to me...unit would run fine until about 3pm then freeze up. They had to drain the unit, replace the TEV and restart.
|
|
|
Commercial Industrial HVAC Tech.
Like stated before. Lack of air flow (dirty filter or bad blower motor). Non-condensables in the system. Ice pellits will form (water vapor in the system) and cause a restriction causing a pressure drop and the system can freeze up. This would explain why you could thaw out the AC and it will be fine for a little or a long while. It depends. Low refrigerant. Again causing a pressure drop and the system will freeze. Freon is now like liquid gold in a bottle. Wholesale houses are charging anywhere between $750 and $950 for a 30lb jug of R-22. Depending how low the system is and where the leak is at, your going to have to make a decision. Hope this helps OP. Sean |
|
|
I would check the air flow over the coils first, low coolant levels will cause short cycling and cause the compressor to overheat and then shutting off on high pressure. I'm not a HVAC guy but I do have a jounrneymans license for commercial refrigeration, both freon and ammonia, the principals are the same, low coolant level won't cause freezing of the coils, low coolant will be first noticed by warmer air from the registers, followed by high pressure shut offs. Generally your coils freeze up from inadequate air flow over the coils during defrost, you may also have a malfunctioning timer. First thing to try is shut it down, wait until the ice has melted, than restart it and when it starts to freeze up put a fan on the coils and see if that helps. Your defrost fan may be malfunctioning causing insuffiect air flow. Your freon levels may be low, but when ever a "tech" shows up the standard reply is freon leak, and they do loose some, but generally a leak means you loose it all, the reason your low after a freeze up is the compressor gets hot and as the pressures increase they will release some to lower the pressure through a high pressure regulator or else something's going to blow apart. Check your temps at the register that is the surest way and easiest way to check if your output.
|
|
The air is always cold, I checked the evaporator coils, they were dirty. I've cleaned them and turned her on again. Keeping a close eye on it, hopefully that will do the trick and I won't be out a bunch of money.
|
|
|
What are the symptoms when the A/C freezes up? I have an updraft unit, I am pretty sure that sucks to check the coils on.
|
|
Quoted:
The air is always cold, I checked the evaporator coils, they were dirty. I've cleaned them and turned her on again. Keeping a close eye on it, hopefully that will do the trick and I won't be out a bunch of money. View Quote |
|
What's the weather been like? A low ambient/ load condition can case it to freeze up. Do you have a humidifier that's still on and should be shut down for the season?
Generally residential AC. Is designed to run when it's 65*F or higher ,unless it is set up control wise when the temps outside are lower. What do you have the indoor temp set to? Sometimes during the spring time it can get warm enough and, humid enough and people will turn on the AC. Temp at night may the drop below design running temp. Could freeze up. Just some things to consider. |
|
Quoted:
+1 to the low on coolant responses. to thaw it out, just run it on fan for a few hours. that'll buy you some time before the a/c guy comes over. he can't troubleshoot/fix it if your coil is frozen over so might as well start thawing it. View Quote |
|
Same thing happened to mine this year on a 5 year old house and the leak ended up being a bad coil in the air handler. They replaced the entire air handler under warranty.
|
|
|
|
I just recently had a bad relay causing the bower fan to not come on every time it was called. It would eventually come on, but sometimes only after no airflow caused the evaporator coil to freeze.
|
|
If it froze up you're leaking.
I went through it twice last summer and am about to pay 6500 for new shit. |
|
Either evaporator coils are dirty or low freon.
The first place I'd check for leaks are the Schrader valves on the CU. |
|
Quoted:
If it froze up you're leaking. I went through it twice last summer and am about to pay 6500 for new shit. View Quote |
|
|
|
It was an airflow issue, and has been resolved.
Thanks everyone. |
|
|
We had a power outage last month during a storm in which it flickered on/off before staying off.
This caused the contactor on the compressor to get stuck so it couldn't shut off. This caused the coil to freeze up. So OP, is you compressor running all the time? If yes, it may be the contactor. |
|
Dirty blower dirty coil fan running wrong direction fan running slow low charge
|
|
Quoted:
If it froze up you're leaking. I went through it twice last summer and am about to pay 6500 for new shit. View Quote |
|
|
Quoted:
@Riley1980 There is a kind of filter over the coils as well, it was dirty, so I cleaned it and wiped the coils down. No more issues. View Quote View All Quotes View All Quotes |
|
I had this issue as well and it ended up being some sort of regualtor/valve that allows a certain amount of coolant to flow through the coils. (sorry forgot the name) Anyway, it was malfunctioning and stuck wide open causing the coils to freeze over. Replaced and no issues since.
|
|
Quoted:
I had this issue as well and it ended up being some sort of regualtor/valve that allows a certain amount of coolant to flow through the coils. (sorry forgot the name) Anyway, it was malfunctioning and stuck wide open causing the coils to freeze over. Replaced and no issues since. View Quote (Thermal expansion valve) Pretty common issue, depending on the quality of install. |
|
Quoted:
Commercial Industrial HVAC Tech. Like stated before. Lack of air flow (dirty filter or bad blower motor). Non-condensables in the system. Ice pellits will form (water vapor in the system) and cause a restriction causing a pressure drop and the system can freeze up. This would explain why you could thaw out the AC and it will be fine for a little or a long while. It depends. Low refrigerant. Again causing a pressure drop and the system will freeze. Freon is now like liquid gold in a bottle. Wholesale houses are charging anywhere between $750 and $950 for a 30lb jug of R-22. Depending how low the system is and where the leak is at, your going to have to make a decision. Hope this helps OP. Sean View Quote |
|
Quoted:
Could be anywhere. But usually it's the outside coils. The constant vibration from the compressor eventually causes a tear. If your installer didn't put your unit on vibration dampers it's practically a guarantee. View Quote |
|
Quoted:
we replace a 100 or more evaporator coils for every condensor coils we replace View Quote View All Quotes View All Quotes Quoted:
Quoted:
Could be anywhere. But usually it's the outside coils. The constant vibration from the compressor eventually causes a tear. If your installer didn't put your unit on vibration dampers it's practically a guarantee. |
|
Quoted:
we replace a 100 or more evaporator coils for every condensor coils we replace View Quote View All Quotes View All Quotes Quoted:
Quoted:
Could be anywhere. But usually it's the outside coils. The constant vibration from the compressor eventually causes a tear. If your installer didn't put your unit on vibration dampers it's practically a guarantee. |
|
Quoted:
Could be a lot of things. Cheapest easiest is air flow (filter). Next thing I would check is the Evap coil itself being dirty, not allowing air to pass. Then superheat/subcool to check Refrigerant levels, txv (if applicable) operation, and for an over/under charge. Systems don't usually just start leaking out of the blue... Unless it's a shrader valve. Then look for non condensables in the system. Generally speaking, evap coil freezing up means the system is to cold, so it's not pulling enough air through it to evaporate the refrigerant. Or possibly incorrectly charged, (pressure/temperature relationship). It's hard to diagnose without the proper tools. Eta: YMMV, everyone has their own opinion/experience. View Quote |
|
Quoted:
Could be a lot of things. Cheapest easiest is air flow (filter). Next thing I would check is the Evap coil itself being dirty, not allowing air to pass. Then superheat/subcool to check Refrigerant levels, txv (if applicable) operation, and for an over/under charge. Systems don't usually just start leaking out of the blue... Unless it's a shrader valve. Then look for non condensables in the system. Generally speaking, evap coil freezing up means the system is to cold, so it's not pulling enough air through it to evaporate the refrigerant. Or possibly incorrectly charged, (pressure/temperature relationship). It's hard to diagnose without the proper tools. Eta: YMMV, everyone has their own opinion/experience. View Quote |
|
Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!
You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.
AR15.COM is the world's largest firearm community and is a gathering place for firearm enthusiasts of all types.
From hunters and military members, to competition shooters and general firearm enthusiasts, we welcome anyone who values and respects the way of the firearm.
Subscribe to our monthly Newsletter to receive firearm news, product discounts from your favorite Industry Partners, and more.
Copyright © 1996-2024 AR15.COM LLC. All Rights Reserved.
Any use of this content without express written consent is prohibited.
AR15.Com reserves the right to overwrite or replace any affiliate, commercial, or monetizable links, posted by users, with our own.