7/5/2017 11:07:24 AM EDT
This is the second time this has happened.

I was trying to sleep and noticed that it seemed warm in the house.  The fan for the AC was running, but the air coming out wasn't cold.  I checked the breakers, and everything was on.  I flipped off the breakers for the AC only (not including the fan), waited, and flipped them back on.  As I did that, I could hear the AC unit on the roof start up.  I went back inside and noticed that the air coming from the ducts was cool.  I did the same procedure a day or two earlier with the same results.

Any ideas of what could be causing this?

I live in NM and have a flat roof on my house.  I don't like it, but we usually don't get that much rain or snow.
7/5/2017 11:14:27 AM EDT
[#1]
Fault with outdoor unit, brain is locking it out and you're resetting fault lockout by cutting power. Might be a good idea to call someone if it happens again. It's trying to tell you something
7/5/2017 11:14:42 AM EDT
[#2]
Might be a bad start/run capacitor on the condenser unit outside.  In simple terms the capacitor is what gives the compressor a 'jolt' of electricity too start up because they draw quite a few amps on startup.
7/5/2017 11:18:31 AM EDT
[#3]
If it does it again, before you reset the breakers, go outside and see if the outside unit is running.

If not, start there. If your capacitor has a swolen up looking top like a can about to explode, there is your problem.

Matter of fact just go look at the capacitor and see if the top is still flat.
7/5/2017 11:23:22 AM EDT
[#4]
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
7/5/2017 11:29:26 AM EDT
[#5]
Quote History
Quoted:
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
View Quote
I've never seen a residential one mounted on the roof up here but every Walmart/stores like that all have them roof mounted
7/5/2017 11:45:24 AM EDT
[#6]
Outside capacitor is bad or fan motor is getting ready to shit the bed.
7/5/2017 1:00:46 PM EDT
[#7]
Quote History
Quoted:
I've never seen a residential one mounted on the roof up here but every Walmart/stores like that all have them roof mounted
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
I've never seen a residential one mounted on the roof up here but every Walmart/stores like that all have them roof mounted
Attached File
7/5/2017 1:03:06 PM EDT
[#8]
Quote History
Quoted:
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
View Quote
i have seen a lot of them on older hoses in Vegas and in Cali.
7/5/2017 1:36:24 PM EDT
[#9]
Quote History
Quoted:


I've never seen a residential one mounted on the roof up here but every Walmart/stores like that all have them roof mounted
View Quote
Could be worse-down the street from us we have newly built $500-600K townhouses with the outside units 4-5 feet from the exterior wall and visible in the lower third of the walk out basement window.
7/5/2017 2:21:43 PM EDT
[#10]
EDIT: Removed and re-posted correctly due to non-functioning gray-matter...
7/5/2017 2:25:42 PM EDT
[#11]
Are you positive the breaker wasn't tripped?  If a breaker is tripped, the little 'switch' will still be in the on position.  Turning it off, then back on again will reset a tripped breaker.

I had this same exact issue, and it ended up being a bad breaker that would only trip sometimes.
7/5/2017 2:26:23 PM EDT
[#12]
Lol at the capacitor comments. Resetting it won't reset a capacitor. It will reset a safety control.

Could be a lot of things people.  Call a hvac tech.
7/5/2017 2:27:47 PM EDT
[#13]
Quote History
Quoted:
Might be a bad start/run capacitor on the condenser unit outside.  In simple terms the capacitor is what gives the compressor a 'jolt' of electricity too start up because they draw quite a few amps on startup.
View Quote
My first thought. 
7/5/2017 2:29:17 PM EDT
[#14]
Quote History
Quoted:
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
View Quote
My wife's grandma's is on her roof in Florida. She has to get it replaced and it's going on the ground.
7/5/2017 2:30:32 PM EDT
[#15]
Quote History
Quoted:
Fault with outdoor unit, brain is locking it out and you're resetting fault lockout by cutting power. Might be a good idea to call someone if it happens again. It's trying to tell you something
View Quote
The above is likely.  Resetting removes the fault and removes the fault code.  If it happens again do not reset the power.  Call someone in to look at the condenser in failure mode.
7/5/2017 2:41:11 PM EDT
[#16]
Quote History
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
I can't help with your problem, but I have a question.

Why is your unit on the roof?  I have seen this on home improvement shows.  What I assume is the compressor unit mounted on the roof, in full sun.

This must be a western US thing, I have never seen one mounted on a roof down south.

Why?
I've never seen a residential one mounted on the roof up here but every Walmart/stores like that all have them roof mounted
https://www.AR15.Com/media/mediaFiles/295532/freon-410a-21-246664.JPG
From what I've seen in AZ, the roof mounted A/C units have usually replaced a swamp cooler (evap. cooling) that was installed when the house was built.  I haven't seen many, if any new builds that have the condenser on the roof.
7/5/2017 2:43:19 PM EDT
[#17]
Quote History
Quoted:
Lol at the capacitor comments. Resetting it won't reset a capacitor. It will reset a safety control.

Could be a lot of things people.  Call a hvac tech.
View Quote
You and the 1st poster are the only 2 that have a clue.It's always the capacitor to these backyard a/c mechanics.If it comes back on after you cycle power you are resetting the comp. lockout board/relay.On many units when a safety trips it will lock the system out so no further damage is done.With the 110+ temps In your area it's a good bet the high pressure switch is taking it out.                                                            "But I replaced the capacitor and it started working!"And even a blind squirrel finds an acorn every now and then.
7/5/2017 2:46:37 PM EDT
[#18]
Quote History
Quoted:
Might be a bad start/run capacitor on the condenser unit outside.  In simple terms the capacitor is what gives the compressor a 'jolt' of electricity too start up because they draw quite a few amps on startup.
View Quote
Our A/C Unit was doing the same thing.

One "Capacitor" and 2 hours of service call (included travel time) fixed it.

Here in Kali, about $80.00 Total Price.
7/5/2017 2:51:38 PM EDT
[#19]
Quote History
Quoted:


i have seen a lot of them on older hoses in Vegas and in Cali.
View Quote
We chose to have ours mounted on the ground, next to the house. (Cali, add-on unit)

It takes up space, and I could see where some people would rather
have the unit on the house, because it takes up a 36" X 36" foot print.

Also, the noise that one hears inside the house is prob is prob less
when mounted on the roof.
7/5/2017 5:12:44 PM EDT
[#20]
Quote History
Quoted:
We chose to have ours mounted on the ground, next to the house. (Cali, add-on unit)

It takes up space, and I could see where some people would rather
have the unit on the house, because it takes up a 36" X 36" foot print.

Also, the noise that one hears inside the house is prob is prob less
when mounted on the roof.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:


i have seen a lot of them on older hoses in Vegas and in Cali.
We chose to have ours mounted on the ground, next to the house. (Cali, add-on unit)

It takes up space, and I could see where some people would rather
have the unit on the house, because it takes up a 36" X 36" foot print.

Also, the noise that one hears inside the house is prob is prob less
when mounted on the roof.
I watched some A/C guys installing a new split system and they were mounting the condenser on the roof.  I asked them why and they told me they get stolen on the ground.  Thieves cut the wires and lineset and just wheel it away on a handtruck.  It only takes minutes.
7/5/2017 5:21:43 PM EDT
[#21]
Is your unit equipped with a condensate overflow switch? I had a clogged condensate drain line activate the switch and would only get warm air.
7/5/2017 5:30:42 PM EDT
[#22]
Quote History
Wonder how that complicates a roof replacement?
7/5/2017 5:54:57 PM EDT
[#23]
As a general rule, commercial units are roof mounted due to their size and less work/materials on new construction.
The trunk lines are directly underneath and less copper to run.
If mounted on the ground of a big biz, they would need to be scattered around for different zones and would take up valuable real estate.

Some specialty cooling units are ground mounted and put in one area to stay self contained.
7/5/2017 6:48:33 PM EDT
[#24]
Quote History
The giant duct screams swamp cooler.
7/5/2017 6:53:52 PM EDT
[#25]
Roof mounted A/C is fairly common here in Vegas, although the newer stuff is mostly ground units.
7/5/2017 6:58:56 PM EDT
[#26]
Quote History
Quoted:
You and the 1st poster are the only 2 that have a clue.It's always the capacitor to these backyard a/c mechanics.If it comes back on after you cycle power you are resetting the comp. lockout board/relay.On many units when a safety trips it will lock the system out so no further damage is done.In your area it's a good bet the high pressure switch is taking it out.                                                            "But I replaced the capacitor and it started working!"And even a blind squirrel finds an acorn every now and then.
View Quote
yup. its funny to watch homeowners tell what the problem is over the internet.  pays to know commercial HVAC and refrigeration, but hey what do i know.
this is a guessing game to make yourself feel better because you want to think its something stupid and cheap. which it could be, your tstat could be shitting the bed and killing power to not energize the contactor which would shut the compressor off.... call a tech.