2/20/2017 9:52:09 PM EDT
Do I need to upsize my gas line?

I added a 90k BTU furnace last year and now we're adding a 62k BTU gas range.  I'm worried my 3/4" line is too small

EDIT: The 2" is a typo. I meant 8" according to the contractor that moved our meter a couple weeks ago.





UPDATE:

So I downloaded Size-It software and this is what it came up with for a 1.5" WC Overall Pressure Drop. Looks like if I use 3/4" to my drop down the wall for my new range I'll be okay, right?

2/20/2017 9:56:06 PM EDT
[#1]
My brother just had a similar issue.  The solution to not increasing the line size was to increase the service pressure.
2/20/2017 9:57:07 PM EDT
[#2]
Are you sure that's 2 inch wc pressure. Do you have regulators at the appliances?
2/20/2017 10:02:02 PM EDT
[#3]
I think you are okay. Most of your lines are larger, just that 10' of 3/4" supporting both appliances. But I don't know how much you can add to one gas line regardless of size before you run in capacity problems.

You probably need to talk to someone that can actually get you a 100% answer.
2/20/2017 10:02:43 PM EDT
[#4]
Quote History
Quoted:
My brother just had a similar issue.  The solution to not increasing the line size was to increase the service pressure.
View Quote
If it won't fit, just push harder! 
2/20/2017 10:05:38 PM EDT
[#5]
I don't remember how to do the calculations, but your layout is pretty standard in most houses that I've seen. It should work, as it is very unlikely you're going to have all burners and the oven going at the same time....while the furnace is also on.
2/20/2017 10:10:40 PM EDT
[#6]
No way gas meter is 2IWC, if regulated it's 7IWC or around 12IWC if non regulated standard pressure. Propane will be 10-11 IWC. With natural gas you need at least 5 IWC at the appliance which will then regulate it down to 3.5IWC at the appliance regulator or gas valve.

what is your total house load, I am guessing you have a standard 250 meter on the house and no elevated pressure. [due to a large generator or other high demand device]
2/20/2017 10:51:40 PM EDT
[#7]
Quote History
Quoted:
No way gas meter is 2IWC, if regulated it's 7IWC or around 12IWC if non regulated standard pressure. Propane will be 10-11 IWC. With natural gas you need at least 5 IWC at the appliance which will then regulate it down to 3.5IWC at the appliance regulator or gas valve.

what is your total house load, I am guessing you have a standard 250 meter on the house and no elevated pressure. [due to a large generator or other high demand device]
View Quote
Yeah, I thought he might have mistaken 2 inches for 2 pounds, but probably not with those pipe sizes. The only place that seems like it would be an issue, (without looking at a chart), is the oven and the furnace off of the 3/4" line.
2/20/2017 11:05:40 PM EDT
[#8]
You'll be fine.
2/20/2017 11:06:12 PM EDT
[#9]
Your service pressure downstream of the regulator should be 12" w.c. for all residential application.

If sized exact per code, your 3/4" pipe is probably undersized.  However, it is most unlikely you would have all appliances running @ max output simultaneously and remember the pressure drop shown in Table 402 is a total of 0.3" w.c.  Your appliance needs 7" w.c. to operate.  There is plenty of "spare".  No need to worry.

International Plumbing Code - Gas piping table
2/20/2017 11:11:53 PM EDT
[#10]
at 2psi you have tons of gas, just put your regulator at the appliance. normal is 1/4lb (7iwc) your over length.... but it'd work, can you take off of the 1"
2/20/2017 11:51:12 PM EDT
[#11]
Quote History
Quoted:
Are you sure that's 2 inch wc pressure. Do you have regulators at the appliances?
View Quote


No I'm not sure, lol that was a typo. I meant 8" but guess I screwed up the 10 key.
2/21/2017 12:44:20 AM EDT
[#12]
Upsize all the pipes to 2" and have an AL1000 installed just incase you want to run your dryer and one burner on the stove at the same time
2/21/2017 1:17:34 AM EDT
[#13]
Why not have a manifold where the main line enters the house, and then run separate lines from there to each appliance, instead of having a branching arrangement? My house has black iron pipe from the meter through the wall into the basement, where the manifold is located. From there, separate copper lines run to the furnace, water heater, and stove. I believe the copper pipe is 1/2" or 3/4", depending on the appliance. (The furnace has the larger pipe size.) There are a couple of more unused connections still available at the manifold.
2/21/2017 8:45:19 AM EDT
[#14]
Quote History
Quoted:
Why not have a manifold where the main line enters the house, and then run separate lines from there to each appliance, instead of having a branching arrangement? My house has black iron pipe from the meter through the wall into the basement, where the manifold is located. From there, separate copper lines run to the furnace, water heater, and stove. I believe the copper pipe is 1/2" or 3/4", depending on the appliance. (The furnace has the larger pipe size.) There are a couple of more unused connections still available at the manifold.
View Quote


Because I'd rather not repipe everything if I don't need to.....
2/21/2017 11:44:46 AM EDT
[#15]
So I downloaded Size-It software and this is what it came up with for a 1.5" WC Overall Pressure Drop. Looks like if I use 3/4" to my drop down the wall for my new range I'll be okay, right?

2/21/2017 11:58:25 AM EDT
[#16]
Yes no worries