9/5/2013 9:54:52 AM EDT
We have a bank of two elevators that we took for maintenance a while back that have been problematic. We recently realized that the supply voltage to the cars is 208vac 3ph, when it requires 230vac 3ph. We could see brakes drop and drive faults when the voltage dropped to around 201v

We told the building that the voltage was the problem, and they hired an electrician to install a transformer to make the change.

Each elevator needs 51 amps. I expected to see the electrician wiring in a big ass 35-40kva transformer, but they wired two 7.5 kva boxes in parallel to get a total of 15kva.

This was last night. Today both cars are shutting down.

Am I crazy, or did they vastly undersize their transformer?

Electrically, how do you think this would show up on our end? Undervoltage? I'm thinking melted wires in the long run.
9/5/2013 10:11:26 AM EDT
[#1]
Did they install a boost transformer to go from 208v nominal to 230v?   What is the output voltage to the elevator drive?  Could be several different things.

Posted Via AR15.Com Mobile
9/5/2013 10:13:17 AM EDT
[#2]
they needed to hook up a bost trans. you need alest 20.2 kva ,65amp curcut from 208v  panle 3 phase.,to get 230v / 51amps..
9/5/2013 10:14:35 AM EDT
[#3]
A regular transformer drops voltage...
9/5/2013 10:15:12 AM EDT
[#4]
:Normally the kva rating of the boost is based on the boost voltage and current.  So a 7.5kva boost that has a 21v increase will carry about 65A.  This is dependant on the buck/boost.  Why don't you post a picture of their nameplate?  Would help us after you measure the voltage at the elevator drives.

Posted Via AR15.Com Mobile
9/5/2013 10:15:23 AM EDT
[#5]
check voltage, mostlikly they used old curcut at 208/ 51amps
9/5/2013 10:20:46 AM EDT
[#6]
Quote History
Quoted:
A regular transformer drops voltage...
View Quote


That depends on which way you wire it.
9/5/2013 10:21:21 AM EDT
[#7]
Quoted:
We have a bank of two elevators that we took for maintenance a while back that have been problematic. We recently realized that the supply voltage to the cars is 208vac 3ph, when it requires 230vac 3ph. We could see brakes drop and drive faults when the voltage dropped to around 201v

We told the building that the voltage was the problem, and they hired an electrician to install a transformer to make the change.

Each elevator needs 51 amps. I expected to see the electrician wiring in a big ass 35-40kva transformer, but they wired two 7.5 kva boxes in parallel to get a total of 15kva.

This was last night. Today both cars are shutting down.

Am I crazy, or did they vastly undersize their transformer?

Electrically, how do you think this would show up on our end? Undervoltage? I'm thinking melted wires in the long run.
View Quote


Lots of possible problems there.  The elevator motors are controlled by VFDs.  The drive needs to be properly configured for the motor load and input voltage.   Usually the drive documentation will steer the electrician the right way.

The motors are probably the 9 lead type, and can be wired for different input voltage.  Has that been checked?

Any more info on the type of transformers?
9/5/2013 10:26:27 AM EDT
[#8]
After recently installing a buck/boost transformer I was thinking the same thing but upon close inspection could see that you are only passing like 10% of the current so the "mongo unit" wasn't required.
9/5/2013 10:32:33 AM EDT
[#9]
Unless I'm misreading this, 15kva sounds almost exactly right.
For one elevator.  
9/5/2013 10:44:14 AM EDT
[#10]
Quote History
Quoted:
Unless I'm misreading this, 15kva sounds almost exactly right.
For one elevator.  
View Quote



I may not have described the layout right.

Both cars are fed from these transformers through a single set of lines from the basement. They split in the elevator room to the two disconnects, so both cars are fed from the 15kva transformers.

I read where buck boost can supply more than the rated kva, but every sizing chart I see agrees with my estimates.
9/5/2013 10:47:22 AM EDT
[#11]
Quote History
Quoted:

Lots of possible problems there.  The elevator motors are controlled by VFDs.  The drive needs to be properly configured for the motor load and input voltage.   Usually the drive documentation will steer the electrician the right way.

The motors are probably the 9 lead type, and can be wired for different input voltage.  Has that been checked?

Any more info on the type of transformers?
View Quote


They are 9 lead, and are wired for 208.

The drives can fault out when the line voltage drops below 208, which we have seen. The controller was bought by another company set up for 230. The manufacturer agrees that it needs 230.
9/5/2013 10:49:34 AM EDT
[#12]
Quote History
Quoted:
check voltage, mostlikly they used old curcut at 208/ 51amps
View Quote


We do have 230 now, but may be seeing some weird variations between legs as the cars move. I'm not on site, so I'm getting this second hand.

9/5/2013 10:53:45 AM EDT
[#13]
Quote History
Quoted:
:Normally the kva rating of the boost is based on the boost voltage and current.  So a 7.5kva boost that has a 21v increase will carry about 65A.  This is dependant on the buck/boost.  Why don't you post a picture of their nameplate?  Would help us after you measure the voltage at the elevator drives.

Posted Via AR15.Com Mobile
View Quote


I'm not on site, so I can't get a pic.

Based upon what you have above, it does sound correct...

Hmmm

9/5/2013 10:56:11 AM EDT
[#14]
220/221 Whatever it takes...its all ball bearings these days.
9/5/2013 11:03:17 AM EDT
[#15]
I know that the inter-leg voltage variations spells trouble for the VFD stuff.   My Korean lathe gets pissy if you don't give her the right juice.
9/5/2013 11:07:06 AM EDT
[#16]
http://www.buckboostcalculator.com/index.cfm

Phase: Open Delta
Available Voltage: 208
Voltage Change: 10.00 %
Boost 229
Load Current: 100.85
Calculate from KVA: 40
50Hz Required? 60HZ




This calculator show me a little over 40kva is needed?

Now I'm lost