Thank you for your post. I will certainly go with an exhausted heating unit, I don't need any condensation issues as you mentioned. My shop is insulated with foam board insulation (2" on walls and ceiling). I may add some batting later for additional warmth. My gas line will be a fairly short run, approximately 20 feet from the nearest access to the shop. I have not estimated the cost but I think it will be affordable. The heater I am thinking about is a 30K forced air BTU unit. What do you think about his from your experience?
View Quote
I think 30k would be way too big. You have 288 sq ft. You have around R10 insulation which is a little light....especially for your area....but not bad.
How tall are the walls?
Using the rule of thumb of 40BTU per sq ft you should need roughly 12000 BTU. An 18k through the wall heater at 70% efficiency (most through the wall heaters run between 70-80% efficient...Usually less than 80%) would produce roughly 12.6k BTU of useable heat....depending on the efficiency rating.
I think an 18k would do it and definitely do it if you upped the R value of your insulation....especially in the ceiling.
20 ft run is simple. Definitely do it in natural gas.
Looks like Menards can special order a 22k btu vented heater for $670.