I run my generator monthly for about a half hour. I turn off the fuel and the let the generator die, then top off the fuel. Ive been running it without a load, and was wondering if I should run it with a load during my monthly runs?
5/14/2011 8:54:02 AM EDT
[#1]
YES!  Where we are the humidity is really high. Running under a load is the only real "test".
5/14/2011 11:57:47 AM EDT
[#2]
Yes, you should put a load on it.  I use either a hair dryer , wet dry vac or a small electric heater.
5/14/2011 2:05:30 PM EDT
[#3]
The engine is only half of a generator.  You need to test and work the generator portion during its running.  Doing this helps insure it's in working order when it's needed.  If the generator loses its field it won't make power but the engine will run.



Plug in a space heater or two.  Ideally you want to bring the generator up to 50% load while testing it.
5/14/2011 2:07:18 PM EDT
[#4]
skillsaw
5/15/2011 5:45:09 AM EDT
[#5]
Thanks, I guess Ill run my shop vac (1100 watts) and hot plate (1800 watts) on the next run
5/15/2011 8:41:03 AM EDT
[#6]
Quoted:
Thanks, I guess Ill run my shop vac (1100 watts) and hot plate (1800 watts) on the next run


I run mine and use my shopvac to clean my car, might as well get some use out of the load
5/15/2011 5:23:01 PM EDT
[#7]
Quoted:
Thanks, I guess Ill run my shop vac (1100 watts) and hot plate (1800 watts) on the next run


Your shop vac probably only draws the full 1100 watts when it's working hard (i.e., trying to suck air against a restriction). The rest of the time, it may be only drawing a small fraction of the wattage shown on the nameplate. Most other motor-powered devices are the same way.

Electric space heaters make ideal loads for testing and "exercising" generators - They consistently pull pretty close to their nameplate wattage (provided the thermostat doesn't kick off), and they present a nice, purely resistive load to the generator - no inductance or capacitance is present that can screw up your power measurements.
5/15/2011 5:25:41 PM EDT
[#8]
I use a 500w work light when I check my little 2000w champions. It's enough load to tell in the sound of the motor
5/16/2011 5:00:24 AM EDT
[#9]
Quoted:
Quoted:
Thanks, I guess Ill run my shop vac (1100 watts) and hot plate (1800 watts) on the next run


Your shop vac probably only draws the full 1100 watts when it's working hard (i.e., trying to suck air against a restriction). The rest of the time, it may be only drawing a small fraction of the wattage shown on the nameplate. Most other motor-powered devices are the same way.

Electric space heaters make ideal loads for testing and "exercising" generators - They consistently pull pretty close to their nameplate wattage (provided the thermostat doesn't kick off), and they present a nice, purely resistive load to the generator - no inductance or capacitance is present that can screw up your power measurements.


Actually, with a pump/blower (a shop vac is just a big air blower) it's the contrary. The largest load on the motor is when there isn't a restriction, ie, it's pumping the most air it can possibly pump. If you cover the hose with you hand you'll notice the motor takes a big jump in RPMs, that is because the load on the motor is reduced to a very small amount.
5/16/2011 7:31:23 PM EDT
[#10]
Quoted:
Quoted:
Quoted:
Thanks, I guess Ill run my shop vac (1100 watts) and hot plate (1800 watts) on the next run


Your shop vac probably only draws the full 1100 watts when it's working hard (i.e., trying to suck air against a restriction). The rest of the time, it may be only drawing a small fraction of the wattage shown on the nameplate. Most other motor-powered devices are the same way.

Electric space heaters make ideal loads for testing and "exercising" generators - They consistently pull pretty close to their nameplate wattage (provided the thermostat doesn't kick off), and they present a nice, purely resistive load to the generator - no inductance or capacitance is present that can screw up your power measurements.


Actually, with a pump/blower (a shop vac is just a big air blower) it's the contrary. The largest load on the motor is when there isn't a restriction, ie, it's pumping the most air it can possibly pump. If you cover the hose with you hand you'll notice the motor takes a big jump in RPMs, that is because the load on the motor is reduced to a very small amount.


True, the impeller is stalling aerodynamically when too a great a differential pressure is attempted to be developed.

For example, the last compressor stage of a PT6 uses a 'bleed air' 'control' to regulate pressure at the input of the blades to prevent 'stalling'.