6/20/2009 9:40:23 AM EDT
My central AC fan won't quit running.



The outside unit kicks in and the house cools off fine but the fan won't stop running until I turn the power off to the fan.





I have a Lennox Pulse 21 furnace model G21Q3-80-3

The outside unit is a Lennox HD25-261-1P



I have replaced the thermostat today after following a troubleshooting guide from here

http://www.inspect-ny.com/aircond/aircond15e.htm#ACNoStart2



What else do I check before I call for professional help or start hitting things with a hammer, the last part was the wife's' idea
6/20/2009 9:42:06 AM EDT
[#1]
Check for corroded contacts to the fan or a bad relay(this more than likely).
6/20/2009 9:57:31 AM EDT
[#2]
I've worked hvac for years and always leave the indoor fan running year round...what year is your systm?... sounds like the fan relay is stuck closed
6/20/2009 10:05:26 AM EDT
[#3]
OK, am I looking for the relays on the fan motor or on a circuit board?





Should I be taking pictures?
6/20/2009 10:09:27 AM EDT
[#4]
If the relay is on the circuit board you gonna have to buy a whole new board.....taking power completely off the system and ohm the relay it should show open if not your contacts in the relay are stuck closed...I just looked over the info on your system and you have a pulse furnace they are notorious for heat exchanger failure so get yours checked every year and get CO detectors nothing like going to sleep and never waking up..
6/20/2009 10:12:21 AM EDT
[#5]
Quoted:
OK, am I looking for the relays on the fan motor or on a circuit board?


Should I be taking pictures?


pics help. the relay will be controlled by the circuit board assy. It will be seperate from the fan and the board trace out the wires from the fan on back and this will lead you to the relay.
6/20/2009 10:43:38 AM EDT
[#6]







From the other side





This is as far out as I can pull the circuit board mount, the air intake pipe is in the way.
We had a fairly heavy thunderstorm this last week, could a voltage spike be causing this problem or would the whole thing refuse to run then?


 
6/20/2009 11:08:10 AM EDT
[#7]
I do see what I believe to be a relay on the board..... You gotta trace out the wires from the fan back. The stuff not on the board looks to be(left to right) a transformer, motor starter and a terminal strip.
6/20/2009 11:09:12 AM EDT
[#8]
Do you have any means to an ohm meter if so check on the relay com. to blue (should be the hi speed fan) make sure you remove the wire from the relay or you'll get a false reading com. should be white thats the other leg of power...one leg hot to the motor all the time and the other leg is the speed on the motor low for heat and hi for cooling, you have to remove the wires from the relay and ohm the contacts cause if you don't you'll ohm thru the motor and get a false reading...and it's really hard telling that a storm could cause this you at least have the inside fan working and that's a good thing you can buy some time into looking for a replacement board...Good Luck!!
6/20/2009 11:11:41 AM EDT
[#9]
Check the relay transformer. Thunderstorms are notorious for frying them out.
6/20/2009 11:16:35 AM EDT
[#10]
relay is stuck on the board which is a common problem
6/20/2009 1:09:10 PM EDT
[#11]


Are you referring to the blower motor or the fan blade on top of your ac unit?

6/20/2009 3:30:31 PM EDT
[#12]
I'd like to thank you guys for your help, it's working as it should now.




6/20/2009 3:35:59 PM EDT
[#13]
Quoted:
I'd like to thank you guys for your help, it's working as it should now.




What was wrong with it?
6/25/2009 2:47:15 PM EDT
[#14]




Quoted:



Quoted:

I'd like to thank you guys for your help, it's working as it should now.









What was wrong with it?



It must have been a stuck relay.

I took a screwdriver to tap the top of the relays and after the AC caught up cooling the house the fan shut off as it should.

It's been working normally ever since.