Anyone do this recently? I'm looking at a ~65 foot run that will need to be trenched, then ran under a sidewalk. Haven't gotten any quotes yet. Thinking maybe I should rent a trencher, lay the conduit and then let a licensed elec. hook everything up as far as the subpanel in the garage.
View Quote
I ran electric to my workshop when I built it. Here's what I learned during the process:
Trenching: Hire someone with a track-hoe or similar to do the trenching. It's SO MUCH FASTER than renting a trencher yourself. The guy showed up, I told him I needed minimum 24" (roughly the same run as yours). He hooked up a 1' wide bucket, and in 10 or fifteen minutes, had the entire trench dug... to 30+". He also laid the dirt on the edge of the trench very nicely. I hurried and glued and dropped the conduit in the trench, and in another 5 minutes he'd knocked the dirt back in the trench and packed it down a bit. If your conduit is close to ready, you can have the entire affair done in less than 30 minutes. I think it cost me an extra $75 or so above renting a trencher myself, but I didn't have to drive to get the trencher, run the trencher, drive the trencher back, etc..
Conduit: Run bigger conduit than you think you need. Conduit is cheap. Also, while you're at it, throw a second conduit in the trench (this can be smaller) in case you ever want to pull network cable out to the garage for wifi. Don't screw around with direct burial, the slightest nick in the insulation, and it's GOING to fail later. Like I said, conduit is cheap. And if you ever need to pull new cable... conduit makes it a snap. Really, you're only talking another $30 and 10 minutes to use conduit.
Cable/sizing: Run a size or two bigger than you plan on, there's always more to power.
Grounding: You'll need a ground wire run in the conduit, AND a ground rod in the garage.
Pulling the cable: Use pull boxes to keep the cumulative bends between them reasonable, use lube, and it'll pull easy - especially if you've oversized the conduit.
Inspector: Every inspector is different, but in my experience, if you've taken your time in your cabling to cross your Ts, dot your Is, and to DO A NEAT AND TIDY JOB, they'll pick up on it right away, and be a lot less likely to give you trouble. On my inspection, the guy gave a good look in one box, noticed how neat and tidy it all was, then gave a 30-second glance around the room, and said "You're done."
Heating: If you don't have other heating arrangements, you can easily throw 240V com-pak heaters in between the studs of the garage.
Final thought: I put exterior lighting all the way around the exterior of my workshop, and they're controlled with 3-way switches, one in the workshop, one inside the house. If you want to do that (and I do recommend it), run the extra THHN in the conduit for it while you're pulling the main cable.