I'm doing to educational credits for my license and decided I want to learn more about grounding specifically and electrical safety in general

Let's see who's wrong.
2/13/2019 2:03:15 PM EDT
[#1]
Depending on there size of the wire, it will either melt the wire insulation and turn it into what is essentially a heating element until failure of the circuit or trip the breaker.
2/13/2019 2:04:06 PM EDT
[#2]
Tag just out of curiosity.  Make sure ground rod is deep enough!
2/13/2019 2:04:58 PM EDT
[#3]
What kind of OCPD is being implemented?
2/13/2019 2:06:22 PM EDT
[#4]
Worms pop out of the ground.  

Then you go fishing
2/13/2019 2:06:41 PM EDT
[#5]
Quote History
Quoted:
Depending on there size of the wire, it will either melt the wire insulation and turn it into what is essentially a heating element until failure of the circuit or trip the breaker.
View Quote
Unless it's on a GFCI, which should trip.

So my answer is "not enough information provided".
2/13/2019 2:06:55 PM EDT
[#6]
In my universe, it goes BOOM and takes out all the electrical power to a small city.  But then again, in my world, superheroes are real, as are dinosaurs and winning lottery tickets.
2/13/2019 2:06:55 PM EDT
[#7]
Quote History
Quoted:
Worms pop out of the ground.  

Then you go fishing
View Quote
Came to say this lol
2/13/2019 2:06:56 PM EDT
[#8]
If you're asking on here, you should not play with electricity.
2/13/2019 2:07:51 PM EDT
[#9]
Plenty of variables to figure out including the following:

1) Is the system grounded?
2) Conductivity of the dirt between the rod you would energize & the grounding electrode & electrode wire at the panel

-distance will affect this

-moisture & dirt type will to
3) Condition(s) of maintenance of the OCPD...

...Oh, and it is a nominal voltage of 120v
2/13/2019 2:07:59 PM EDT
[#10]
It's kind of like asking, "what happens if I hold on to this 120v wire".
2/13/2019 2:09:33 PM EDT
[#11]
Quote History
Quoted:
If you're asking on here, you should not play with electricity.
View Quote
So you don't know?
2/13/2019 2:09:35 PM EDT
[#12]
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.  There is no resistance to the current path so amperage goes up until the breaker trips. If the wire size is not large enough to accommodate the current it starts to act like a resistor to give off the excess energy in the form of heat and burns up.
2/13/2019 2:10:09 PM EDT
[#13]
I've smoked the wiring on equipment more than once in my life.

Stupidly we hooked up a  ~90Amp 460V pressure washer up to the mains without a neutral with 1000Amp breakers to just run a short test.

That one was a huge mistake. It did things that I can't explain to this day. The pressure hose, which is rubber coated wire braid hose, shorted out on the trailer and burned a hole in the rubber coating and started sparking. I was holding the hose with no current getting to me.

The heating elements all blew out. They were shorted on the inside due to salt water.

Crazy, but the guy that hooked it up didn't use the ground and I didn't know it.
2/13/2019 2:11:01 PM EDT
[#14]
Quote History
Quoted:
Unless it's on a GFCI, which should trip.

So my answer is "not enough information provided".
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Depending on there size of the wire, it will either melt the wire insulation and turn it into what is essentially a heating element until failure of the circuit or trip the breaker.
Unless it's on a GFCI, which should trip.

So my answer is "not enough information provided".
These two answers,combined, are correct. There’s not a lot of info in the OP but:
1. if a GFCI is installed it will trip immediately. If not, then
2. if a breaker or fuse is in the circuit it will trip within seconds. If not then
3. wire will produce heat, followed by smoke, followed by sparks (maybe).

In any case it will be over shortly.
2/13/2019 2:11:03 PM EDT
[#15]
Quote History
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.
View Quote
Except that isn't the same and isn't always what happens in OP's example.
2/13/2019 2:11:42 PM EDT
[#16]
Quote History
Quoted:
Depending on there size of the wire, it will either melt the wire insulation and turn it into what is essentially a heating element until failure of the circuit or trip the breaker.
View Quote
If the breaker and wiring are properly sized, it should just result in a tripped breaker.
2/13/2019 2:13:17 PM EDT
[#17]
Is the ground rod actually grounded?
2/13/2019 2:14:37 PM EDT
[#18]
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.  There is no resistance to the current path so amperage goes up until the breaker trips. If the wire size is not large enough to accommodate the current it starts to act like a resistor to give off the excess energy in the form of heat and burns up.
View Quote
Quoted:

These two answers,combined, are correct. There’s not a lot of info in the OP but:
1. if a GFCI is installed it will trip immediately. If not, then
2. if a breaker or fuse is in the circuit it will trip within seconds. If not then
3. wire will produce heat, followed by smoke, followed by sparks (maybe).

In any case it will be over shortly.
View Quote
Quoted:

If the breaker and wiring are properly sized, it should just result in a tripped breaker.
View Quote
I am not an electrician nor do I claim any ability to know wiring.  That's why watching Mike Holt learn me up on grounding ended up very different than I expected.

Watch the first 1:15 of this video-

6 of 7 Grounding Myths (26min:55sec)
2/13/2019 2:14:52 PM EDT
[#19]
If it's pushed into the ground, worms will come out.
2/13/2019 2:15:05 PM EDT
[#20]
Quote History
Quoted:
Is the ground rod actually grounded?
View Quote
At least as well as this one.  
Attached File
2/13/2019 2:15:10 PM EDT
[#21]
Quote History
Quoted:
Except that isn't the same and isn't always what happens in OP's example.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.
Except that isn't the same and isn't always what happens in OP's example.
Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.  If you are installing a grounding rod you are to drive it to a point in the ground where there is moisture so that it does act as a earth ground.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
2/13/2019 2:15:18 PM EDT
[#22]
Quote History
Quoted:

If the breaker and wiring are properly sized, it should just result in a tripped breaker.
View Quote
Yeah but do you ever properly size wire when you run it straight to ground and create a direct short?
2/13/2019 2:15:47 PM EDT
[#23]
If there is a breaker somewhere in the circuit, it should trip the breaker due to the maximum current being exceeded.  If it was connected directly to the meter base with no breaker in the path, it most likely would exceed the current rating of the wire by a very significant margin assuming there is a good connection to ground.  This would result in a melted wire and probably a fire.
2/13/2019 2:17:38 PM EDT
[#24]
Quote History
I promise you that it doesn't even surprise me one bit.

Someone told a worm to ground the generator and that is what they did.
2/13/2019 2:18:51 PM EDT
[#25]
Quote History
Quoted:
Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.
Except that isn't the same and isn't always what happens in OP's example.
Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
2/13/2019 2:19:16 PM EDT
[#26]
Are magnets involved???
2/13/2019 2:21:01 PM EDT
[#27]
Quote History
Quoted:
It's kind of like asking, "what happens if I hold on to this 120v wire".
View Quote
Depends on amperage...
2/13/2019 2:21:06 PM EDT
[#28]
Quote History
Quoted:
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.
Except that isn't the same and isn't always what happens in OP's example.
Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
Do you care to explain?
2/13/2019 2:22:17 PM EDT
[#29]
Quote History
Quoted:

Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
View Quote
I have spend hours trying to get the safety guys (of all places generating plants. Seriously it is always generating plants that can't get it) to understand that grounding the generator on a pressure washer via a ground rod provides the path that would allow the operator to get shocked that would not exist otherwise.
2/13/2019 2:23:48 PM EDT
[#30]
Quote History
Quoted:

Do you care to explain?
View Quote
Don't ground generators. The only way to complete the circuit is back to the generator, unless you ground it to the ground and then you create another path that would typically be through a person.
2/13/2019 2:33:20 PM EDT
[#31]
It will depend a great deal on the grounding. In most situations, not a lot will happen. It probably won't even trip the breaker, as it'd be hard to imagine a low enough impedance between the ground and transformer to get to 15+ amps.

My guess; a decent blue spark and some moderate heating of the wires. If this was a circuit experiencing a ground fault and a GFCI was present it would trip the GFCI.
2/13/2019 2:35:22 PM EDT
[#32]
Quote History
Quoted:
Are magnets involved???
View Quote
Yes.  Rotating ones to create the current.  
2/13/2019 2:38:07 PM EDT
[#33]
The space time continuum will be torn open and Hillary will be elected President.

Don't do it.... It's for your Country.
2/13/2019 2:40:53 PM EDT
[#34]
Quote History
Quoted:
Worms pop out of the ground.  

Then you go fishing
View Quote
This if you use one rod for hot and another for neutral.
2/13/2019 2:42:58 PM EDT
[#35]
How would a GFI trip?  There is no leakage to ground, ie no current traveling on the ground wire.  The load IS the ground.
2/13/2019 2:44:42 PM EDT
[#36]
Where's the video???
2/13/2019 2:45:46 PM EDT
[#37]
Quote History
Quoted:

Don't ground generators. The only way to complete the circuit is back to the generator, unless you ground it to the ground and then you create another path that would typically be through a person.
View Quote
I have been been a key player (project/contract manager)  in the contract to install generators in the 300 to 6,000 kva range and every single one had the generator frame grounded to earth ground due to the contract specs and the manufacturer requirement. Even the UPSs have all required an earth ground which isn’t always easy to do. In some installations we had to dig up and install a grounding field.  Some have required those special gell pellets in areas of low moisture.
2/13/2019 2:47:07 PM EDT
[#38]
Quote History
Quoted:
Yeah but do you ever properly size wire when you run it straight to ground and create a direct short?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:

If the breaker and wiring are properly sized, it should just result in a tripped breaker.
Yeah but do you ever properly size wire when you run it straight to ground and create a direct short?
Shit.  Bro, I don't even do V = IR to see how many amps are going to be pulled.  I just post.  It's like shooting from the hip.  But safer.  Yeah, I was seriously surprised by how many people are just milling around you at any given time, after accidentally shooting that one, I just don't do that anymore.

Look, I have a proven track record of setting myself on fire in situations where a smart person, hell even a Nobel Laureate, would have said such an outcome was impossible.  Thus, I'm very cautious around electricity and fire, and especially electricity that is on fire.
2/13/2019 2:47:22 PM EDT
[#39]
My grandpa had a 100 ft. electrical cord with two steel rods on one end.  The wires were wrapped around the end of the rods and taped up with a few layers of electrical tape.

He'd take the out back of the house, stick the steel rods in the damp dirt between the creek and the back porch, clear us kids out of the area and then go inside and plug the other end into an outlet.

The fishing worms would come out of the ground like rain falling from the skies.  Then he'd unplug the electrical cords and holler for us to quickly gather up the stunned worms in the can we carried.

He'd roll his worm cord up, put it away and we'd go fishing.  Never blew the fuses but maybe that was a function of short duration or plenty of resistance due to the distance from rod to rod.
2/13/2019 2:49:03 PM EDT
[#40]
worms rise to the surface
2/13/2019 2:51:04 PM EDT
[#41]
Quote History
Quoted:
I am not an electrician nor do I claim any ability to know wiring.  That's why watching Mike Holt learn me up on grounding ended up very different than I expected.

Watch the first 1:15 of this video-

https://www.youtube.com/watch?v=qNZC782SzAQ
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.  There is no resistance to the current path so amperage goes up until the breaker trips. If the wire size is not large enough to accommodate the current it starts to act like a resistor to give off the excess energy in the form of heat and burns up.
Quoted:

These two answers,combined, are correct. There’s not a lot of info in the OP but:
1. if a GFCI is installed it will trip immediately. If not, then
2. if a breaker or fuse is in the circuit it will trip within seconds. If not then
3. wire will produce heat, followed by smoke, followed by sparks (maybe).

In any case it will be over shortly.
Quoted:

If the breaker and wiring are properly sized, it should just result in a tripped breaker.
I am not an electrician nor do I claim any ability to know wiring.  That's why watching Mike Holt learn me up on grounding ended up very different than I expected.

Watch the first 1:15 of this video-

https://www.youtube.com/watch?v=qNZC782SzAQ
Well, shit, ain't that something.  This is why I usually math first, post second.  Shit.  If I was doing this in real life, and nothing happened with the breaker, fuck, I'd probably just grab the fucking wire, thinking there wasn't any power to it.

You now see why I might have a lot of problems with setting myself, and others, on fire.
2/13/2019 2:55:10 PM EDT
[#42]
Quote History
Quoted:
Yeah but do you ever properly size wire when you run it straight to ground and create a direct short?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:

If the breaker and wiring are properly sized, it should just result in a tripped breaker.
Yeah but do you ever properly size wire when you run it straight to ground and create a direct short?
I don't know.  Do I have an actual charge number for this?  Or is it just like doing some shitty analysis to placate some people on the internet?

In light of what OP just posted, I don't even think we really need 12-3, or whatever it is, for this circuit.  I think we can take a sledge to the wall, yank some wires, run some new ones, and make this whole thing way more efficient, while, at the same time, coming over budget, late on schedule, and with a metric fuckton of gypsum dust.  What's the salvage value of 60 feet of 12-3?  Maybe there's some cost recoup there?
2/13/2019 2:56:55 PM EDT
[#43]
If the ground rod is bonded to neutral, breaker should trip. If it's just a rod pounded into the earth, then the breaker will not trip and you will set up a ground fault with a voltage gradiant on the ground (earth) between the rod and the points the neutral are bonded to earth ground. As others have said, you will make the worms mad.
2/13/2019 2:58:29 PM EDT
[#44]
Quote History
Quoted:
How would a GFI trip?  There is no leakage to ground, ie no current traveling on the ground wire.  The load IS the ground.
View Quote
No, it should trip the GFI because part or all of the return is being bypassed. It is the exact type of situation that GFIs were designed for.

We stopped using GFIs on pressure washers. Too many issues. The code prevents using a relay on the neutral line, but a relay on the neutral that was normally closed and wired so that if the equipment "received" leaked voltage, it opened the neutral circuit and killed the power would "work" as well. I'm sure there is some legitimate reason it isn';t allowed, but it should work.
2/13/2019 2:58:48 PM EDT
[#45]
Quote History
Quoted:
How would a GFI trip?  There is no leakage to ground, ie no current traveling on the ground wire.  The load IS the ground.
View Quote
Because a GFCI uses a current transformer to look for imbalance of current between the Hot and Neutral.  This is any imbalance >= 5mA.   The GFCI trips on a leaked current .   A regular breaker is looking for an Overload Condition to trip on a ground fault at whatever amperage rating it has.  This is why you need a low impedance path for fault current (equipment ground) in order for a regular breaker to be effective.
2/13/2019 3:03:06 PM EDT
[#46]
Not an electrician....

Ground rod hammered into the ground?  I'm guessing the ground/dirt isn't really conductive enough to transmit 110 volts with any reasonable/measurable level of current.

I voted nothing happens.

Now, a bolt of lightning hitting something attached to the ground rod?  Like shit through a goose.  Slightly higher level of voltage.  
2/13/2019 3:03:38 PM EDT
[#47]
Quote History
Quoted:
Shit.  Bro, I don't even do V = IR to see how many amps are going to be pulled.  I just post.  It's like shooting from the hip.  But safer.  Yeah, I was seriously surprised by how many people are just milling around you at any given time, after accidentally shooting that one, I just don't do that anymore.

Look, I have a proven track record of setting myself on fire in situations where a smart person, hell even a Nobel Laureate, would have said such an outcome was impossible.  Thus, I'm very cautious around electricity and fire, and especially electricity that is on fire.
View Quote
I'm not sure I understand your post

The hypothetical was hooking up a hot wire to the ground rod.

It could have been a 4 ft long 20 gauge or a 100ft long 4gauge.

Get it now?

If you are going to do something like that, I suspect proper wire sizing is somewhere after "what you are going to wear to sleep next month" in the rankings of importance for this exercise
2/13/2019 3:04:34 PM EDT
[#48]
Quote History
Quoted:
My grandpa had a 100 ft. electrical cord with two steel rods on one end.  The wires were wrapped around the end of the rods and taped up with a few layers of electrical tape.

He'd take the out back of the house, stick the steel rods in the damp dirt between the creek and the back porch, clear us kids out of the area and then go inside and plug the other end into an outlet.

The fishing worms would come out of the ground like rain falling from the skies.  Then he'd unplug the electrical cords and holler for us to quickly gather up the stunned worms in the can we carried.

He'd roll his worm cord up, put it away and we'd go fishing.  Never blew the fuses but maybe that was a function of short duration or plenty of resistance due to the distance from rod to rod.
View Quote
In that situation he's using the soil as a conductor, with current flowing through the hot and neutral wires. 'Electrical ground' isn't really a factor, here, since the current will have a far lower impedance path between hot and neutral then it will between hot and ground (that is to say, the power plant).

The impedance of the soil is/was high enough that not enough current could flow to trip the breaker. If he set the rods close enough together or the soil was particularly conductive he might have been able to create a low enough impedance circuit to trip the breaker. Instead, he just passed enough current through the soil, and the worms in it, to irritate them and get them to come to the surface. If you set the rods far enough apart, you'd have effectivly a ground fault and current flow would drop very low and not much would happen beyond a couple feet from the hot electrode.

I used to create very high power resistors for testing loading power supplies with a big bowl of water and some salt. You just position your electrodes across from each other and start adding salt till you get the resistance you desire. You can then further fine tune things by moving the electrodes to change the space between them. Same concept, really. Only catch is that water evaporates, so you have to keep an eye on your water level. If it drops, salinity increases and resistance decreases, and things can sort of get away from you pretty quick.
2/13/2019 3:05:43 PM EDT
[#49]
So what's the correct answer?
2/13/2019 3:05:54 PM EDT
[#50]
Quote History
Quoted:
I'm not sure I understand your post

The hypothetical was hooking up a hot wire to the ground rod.

It could have been a 4 ft long 20 gauge or a 100ft long 4gauge.

Get it now?

If you are going to do something like that, I suspect proper wire sizing is somewhere after "what you are going to wear to sleep next month" are in the rankings of importance for this exercise
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Shit.  Bro, I don't even do V = IR to see how many amps are going to be pulled.  I just post.  It's like shooting from the hip.  But safer.  Yeah, I was seriously surprised by how many people are just milling around you at any given time, after accidentally shooting that one, I just don't do that anymore.

Look, I have a proven track record of setting myself on fire in situations where a smart person, hell even a Nobel Laureate, would have said such an outcome was impossible.  Thus, I'm very cautious around electricity and fire, and especially electricity that is on fire.
I'm not sure I understand your post

The hypothetical was hooking up a hot wire to the ground rod.

It could have been a 4 ft long 20 gauge or a 100ft long 4gauge.

Get it now?

If you are going to do something like that, I suspect proper wire sizing is somewhere after "what you are going to wear to sleep next month" are in the rankings of importance for this exercise