2/13/2019 3:07:26 PM EDT
[#1]
Quote History
Quoted:
It's too late.  I've already started the demo.  Is gypsum dust worth anything?  Because there's a lot of it.
View Quote
lol

True enough.
2/13/2019 3:08:48 PM EDT
[#2]
It should trip the breaker as that’s what it’s designed to do.
Attached File
2/13/2019 3:10:00 PM EDT
[#3]
Quote History
Quoted:
Not an electrician....

Ground rod hammered into the ground?  I'm guessing the ground/dirt isn't really conductive enough to transmit 110 volts with any reasonable/measurable level of current.

I voted nothing happens.

Now, a bolt of lightning hitting something attached to the ground rod?  Like shit through a goose.  Slightly higher level of voltage.  
View Quote
The ground is a good, but not great conductor. Even at low voltages (under 20 even) the ground can carry enough current to pick relays. Thats why we are always checking for grounds on our railroad signaling equipment. At 120 volts, the 15 amp breaker won't trip, but the will still be plenty enough current there to kill you. This is one of the reasons working on a live circuit is so dangerous.
2/13/2019 3:11:35 PM EDT
[#4]
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
2/13/2019 3:13:24 PM EDT
[#5]
Quote History
Quoted:
So what's the correct answer?
View Quote
Depending on the type of circuit and size of wire being used from the breaker to the ground rod (because this would be something that is installed by Johnny Jakeleg not an electrician using whatever wire he pulled out of an old jam system he found out by the curb at his neighbors house), it will trip the GFI is so equipped, trip the breaker if the load is enough to over amp the circuit breaker or smoke the wire and kill the circuit by melting the wire.

It isn't going to just create a direct short that will just burn power indefinitely.
2/13/2019 3:13:39 PM EDT
[#6]
2/13/2019 3:13:56 PM EDT
[#7]
You specify 15A.
So is the source coming from a 15A CB?
Or are you stating it is using 14AWG wire?

What's the source?
Inside a panel witht he neutral bonded to the same ground rod?

Or the ground rod is separate from the source?
2/13/2019 3:13:59 PM EDT
[#8]
Quote History
Quoted:
Depends on amperage...
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
It's kind of like asking, "what happens if I hold on to this 120v wire".
Depends on amperage...
And other circuit characteristics...
2/13/2019 3:17:15 PM EDT
[#9]
Quote History
Damn! Something is pulling a helluva load, for a minute anyway.
2/13/2019 3:17:48 PM EDT
[#10]
Quote History
Quoted:
So what's the correct answer?
View Quote
Yellow!...
2/13/2019 3:18:40 PM EDT
[#11]
Quote History
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
View Quote
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
2/13/2019 3:30:46 PM EDT
[#12]
If it's not the SAME ground rod as the incoming power: Nothing significant will happen. While it is "grounded", I think the impedance would be too high to trip the breaker. (unless a GFI is used, as previously mentioned)
"Ground" is great for lightning, but it's not the same thing as "neutral".
2/13/2019 3:35:07 PM EDT
[#13]
Quote History
Quoted:
It will depend a great deal on the grounding. In most situations, not a lot will happen. It probably won't even trip the breaker, as it'd be hard to imagine a low enough impedance between the ground and transformer to get to 15+ amps.

My guess; a decent blue spark and some moderate heating of the wires. If this was a circuit experiencing a ground fault and a GFCI was present it would trip the GFCI.
View Quote
This is the correct answer.

The low amount of current on the ungrounded wire would probably be enough of an imbalance to trip a GFCI as that same current isn't being returned on the grounded conductor wire.
2/13/2019 3:41:32 PM EDT
[#14]
Nightcrawlers lots of nightcrawlers.
2/13/2019 3:46:19 PM EDT
[#15]
I was completely wrong.

I'll be damned.

It doesn't trip the breaker.
2/13/2019 3:49:39 PM EDT
[#16]
Quote History
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
View Quote
Good to see you around again, and you are most correct.  I am bidding on some structure grounding (the work, not the engineering) and decided I wanted to bone up on my grounding knowledge, I was surprised at how wrong I was with 99% of what I thought I knew about grounding.

I'll just be following the guidance of the experts, which I'm clearly not one.  Interesting to me anyway.
2/13/2019 3:50:26 PM EDT
[#17]
Quote History
Quoted:

You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
View Quote
If the wire is sized for a 15 amp circuit, no, nothing is going to happen to the wire. But that's the point; the wire is sized so that if enough current did flow to present a hazard to the wire in the worst case scenario the breaker will trip before the wire insulation fails.

If you connected a short #28 gauge wire or something, it's possible that enough current could flow through ground to cause the wire to fail*. But, without knowing the impedance of this particular grounding and length of wire run it's not possible to calculate the exact current that will flow and thus the absolute minimum sized wire needed.

The 120v value is the voltage of that leg relative to ground and to the neutral tap of the transformer. But neutral and ground aren't really the same thing. The impedance, or resistance if you want to think in terms of DC, between a ground rod and the ground can be quite high. The impedance between the hot leg and a neutral wire is very low, since that loop is formed by copper. Same voltage, potentially very different resistance and thus different currents.

Now, some grounding rods are bonded directly to the neutral. Shorting a hot leg to that grounding rod is just like shorting to the neutral; that will trip your breaker and/or fail your wire. But not all are.

*fail has a particular meaning here. A wire has failed when it has heated enough that the insulation on it is hot enough to melt or deform. The copper itself will continue to conduct quite happily after the insulation has burnt off, but no insulation means a likely short circuit or ground fault which means more heat which can result in a fire.

Always remember; the breakers are there to protect the wire, not the loads. In order for that to work the wire and breakers have to be sized appropriately for each other. This is all in the code. Deviating from the code may still result in a working circuit, but may also present edge cases where your house burns down.
2/13/2019 3:50:33 PM EDT
[#18]
Quote History
Quoted:

This is the correct answer.

The low amount of current on the ungrounded wire would probably be enough of an imbalance to trip a GFCI as that same current isn't being returned on the grounded conductor wire.
View Quote
@swampvol

You're wrong, but don't take it personal.  It looks like 90% of electricians, even good ones, get this wrong.
2/13/2019 3:52:20 PM EDT
[#19]
Quote History
Quoted:

@swampvol

You're wrong, but don't take it personal.  It looks like 90% of electricians, even good ones, get this wrong.
View Quote
Yep. I definitely learned something new today and I'm glad.
2/13/2019 3:52:46 PM EDT
[#20]
Quote History
Quoted:
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
Picture this:

Two 500’ spools of #12 THHN connected together to make it an overall length of 1000’. Connect a cord plug to the two ends of this 1000’ coil of #12. Plug it into a 120v receptacle!

What happens ??
2/13/2019 3:53:13 PM EDT
[#21]
What color paint is on that nut???
2/13/2019 3:56:03 PM EDT
[#22]
Quote History
Quoted:
I was completely wrong.

I'll be damned.

It doesn't trip the breaker.
View Quote
@krpind

Take a look at Mike's longer video, he's got one that's about 1:20 long and yesterday I watched the entire thing.  My background in electrical circuits isn't strong enough to fully grasp what he's talking about in the minutia, but it still was the most interesting boring video I've ever seen.
2/13/2019 3:58:47 PM EDT
[#23]
Quote History
Quoted:

Came to say this lol
View Quote
I used to enjoy watching my grandfather  do this before we went fishing.  I asked him how it worked and he told me "magic"
2/13/2019 4:10:46 PM EDT
[#24]
Quote History
Quoted:
What color paint is on that nut???
View Quote
Fire Engine Red.
2/13/2019 4:14:59 PM EDT
[#25]
Quote History
Quoted:
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
It all depends on your ground electrode impedance at the site of connection and the source.  Is there a low enough impedance on both connections to cause more than 15 amps to flow across the short?  This is also assuming a residential split phase system with the neutral and grounding electrode bonded near the service entrance and this hypothetical connection being made on a separate ground rod somewhere else in the system.

The vast majority of residential grounding electrodes I have seen have fairly high impedance.  Greater than 10 ohms for sure.

I wouldn't try this within a substation fence on a proper grounding grid.  A recent rain storm, salty soils, high water table, and a crew paid by the hour with an grounding electrode tester could make it interesting on practically any system.  And let's not get going on corner grounded delta.  Or counterpoise grounding.
2/13/2019 4:15:32 PM EDT
[#26]

Y'all motherfuckers need Mike Holt!
2/13/2019 4:16:21 PM EDT
[#27]
It depends on ground conductivity and the distance between the ground rod at the power panel and the ground rod the circuit is connected to.

If the ground conductivity is high enough, it'll trip the 15 Amp breaker/fuse. It it's too low, the ground will dissapate the electrical energy as heat. Standing between the two grounds could be hazardous to your health, though.

2/13/2019 4:16:28 PM EDT
[#28]
Quote History
Quoted:

@krpind

Take a look at Mike's longer video, he's got one that's about 1:20 long and yesterday I watched the entire thing.  My background in electrical circuits isn't strong enough to fully grasp what he's talking about in the minutia, but it still was the most interesting boring video I've ever seen.
View Quote
I was able to easily test this due to some test gear we frequently use and it easily reached the ground rod so it was simple to clamp it on and push a button. No film or photographic proof since the electric company would probably frown on it.

I wrongly assumed the ground would pull enough of a load to trip the breakers.

To be honest, I had someone else do it since I'm laid up at home, but it was easily tested and anyone could replicate it I'm sure.

If I were able to do it, I would put a meter on it and see what it pulls.
2/13/2019 4:22:27 PM EDT
[#29]
Quote History
Quoted:

Good to see you around again, and you are most correct.  I am bidding on some structure grounding (the work, not the engineering) and decided I wanted to bone up on my grounding knowledge, I was surprised at how wrong I was with 99% of what I thought I knew about grounding.

I'll just be following the guidance of the experts, which I'm clearly not one.  Interesting to me anyway.
View Quote
I know just enough to be truly dangerous about grounding on the customer side of the meter.  I'm not a building grounding guy.  My career has focused on the utility side.

Grounding is hard.  I agree with you - interesting and plenty to learn still.
2/13/2019 4:27:46 PM EDT
[#30]
Quote History
Quoted:
Picture this:

Two 500’ spools of #12 THHN connected together to make it an overall length of 1000’. Connect a cord plug to the two ends of this 1000’ coil of #12. Plug it into a 120v receptacle!

What happens ??
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
Picture this:

Two 500’ spools of #12 THHN connected together to make it an overall length of 1000’. Connect a cord plug to the two ends of this 1000’ coil of #12. Plug it into a 120v receptacle!

What happens ??
If you're talking about installing a cord cap (plug) onto each of the two wires from the different spools and splicing the other two ends of the two spools together, nothing will happen as the coiled wire will create a lot of resistance thus keeping the circuit breaker from tripping.

Now, if you straighten the wires out so it's one big flat loop then the breaker will trip.
2/13/2019 4:42:04 PM EDT
[#31]
Quote History
Quoted:
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
On the vast majority of ground electrode installations?  Nothing happens.  Most ground electrodes are fairly high impedance connections to the earth.

There are ways to design, install, and test low impedance ground connections.
You can hook a wire from a 15Amp circuit breaker directly to a ground rod and it won't trip the breaker or smoke a small wire? It will just draw power at below 15 amps using the ground as the load consuming the power?
<< Licensed Electrician. I was 99.99% sure this was correct, but wasn't going out on a limb in an Arf thread. Go to far out on a limb in an Arf thread and there's certain to be someone to cut that limb off, whether your right or wrong. I did state early on about the worms coming out though
2/13/2019 4:47:44 PM EDT
[#32]
Please confirm if you are only hooking up the wire coming out of the breaker and the neutral plays no role in this scenario.
2/13/2019 4:49:33 PM EDT
[#33]
Quote History
Quoted:
Please confirm if you are only hooking up the wire coming out of the breaker and the neutral plays no role in this scenario.
View Quote
I cannot confirm that.  Just guess.
2/13/2019 4:52:29 PM EDT
[#34]
Quote History
Quoted:

I am not an electrician nor do I claim any ability to know wiring.  That's why watching Mike Holt learn me up on grounding ended up very different than I expected.

Watch the first 1:15 of this video-

https://www.youtube.com/watch?v=qNZC782SzAQ
View Quote
Thanks for that vid.

14 mins in was especially interesting about not grounding generators or solar arrays.
2/13/2019 4:52:57 PM EDT
[#35]
Quote History
Quoted:

@swampvol

You're wrong, but don't take it personal.  It looks like 90% of electricians, even good ones, get this wrong.
View Quote
In what way?

I have personally done this test with a ground rod driven in fairly wet black soil, and there wasn't enough current to trip a standard breaker. Now that I think about it, there wasn't enough current to even measure on my Fluke clamp on....which does not read into the mA.

Admittedly, I haven't tried it with a GFCI breaker.

Are you saying that it would not produce any current at all?
2/13/2019 5:00:05 PM EDT
[#36]
Quote History
Quoted:
Do you care to explain?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Quoted:
Quoted:
It happens all the time with flooded junction boxes and such; all that happens is the circuit breaker trips.
Except that isn't the same and isn't always what happens in OP's example.
Well, actually I will submit that it is. Earth ground is functionally equlivent to the neutral in the typical 120 vac circuit. If you are using a generator you will see that the generator manufacturer requires you ground the generator. Water in a junction box in the ground is set at earth potential.

Now if you are considering the stupid shit people do, then yes you can come up with other situations.
Do you care to explain?
On which part?  You're wrong all the way around.  I install a shitload of generators, and not once has the manufacturer instructions required me to add an additional ground rod/auxiliary GEC at the generator.  Are you saying that is what you do, or are you just confused between the GEC and bonding?
2/13/2019 5:04:53 PM EDT
[#37]
My 100 amp service has a shutoff/disconnect at the meter on the outside wall.   It then goes into the house on 2AWG service cable.

I want to put two 60 amp sub panels up.  First one in an attached garage but the cable is going to be buried along the house from meter area to the garage. The second sub panel will go in a detached shed.   I’ll run 4 wire and have all the specs for direct burial cable requirements.

I’m going to put a generator (whole house) transfer switch right after the service meter.   Can I put a power splitter or a small main panel that sends power to the house panel, garage panel and then shed panel?

If I’m running a grounding wire with the sub panel cable, how do I set up the grounding system at the panels?

I was going to connect each subpanel back to the main panel in the house and then put a two rod grounding rod system at each subpanel.   I think that’s only required if the panel is detached?

With what I’m describing, what grounding system will be per code?
2/13/2019 5:05:08 PM EDT
[#38]
Quote History
Quoted:

On which part?  You're wrong all the way around.  I install a shitload of generators, and not once has the manufacturer instructions required me to add an additional ground rod/auxiliary GEC at the generator.  Are you saying that is what you do, or are you just confused between the GEC and bonding?
View Quote
Yep, I've only seen the requirement for an additional GEC for a generator when the service neutral is being switched.
2/13/2019 5:08:20 PM EDT
[#39]
Quote History
Quoted:
Yep, I've only seen the requirement for an additional GEC for a generator is when the service neutral is being switched.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:

On which part?  You're wrong all the way around.  I install a shitload of generators, and not once has the manufacturer instructions required me to add an additional ground rod/auxiliary GEC at the generator.  Are you saying that is what you do, or are you just confused between the GEC and bonding?
Yep, I've only seen the requirement for an additional GEC for a generator is when the service neutral is being switched.
From what I have read, that is correct.  It depends on whether the generator is internally grounding or not (I think I got that word right).  That decides if you switch neutral on the safety transfer switch.  It also decides if the generator has its own grounding rod.   If I remember correctly, the code does require a grounding rod with certain generator types.
2/13/2019 5:10:51 PM EDT
[#40]
Quote History
Quoted:

From what I have read, that is correct.  It depends on whether the generator is internally grounding or not (I think I got that word right).  That decides if you switch neutral on the safety transfer switch.  It also decides if the generator has its own grounding rod.   If I remember correctly, the code does require a grounding rod with certain generator types.
View Quote
Separately derived system.
2/13/2019 5:10:58 PM EDT
[#41]
OP, in a similar manor, say a line falls from the pole. A live line on the ground will not trip any fuses or breakers as the current flow, while signifigant for danger is not enough to likely ever open a safety device like a fuse or breaker. What happens is a ground fault as I alluded to in one of  my previous posts. These are dangerous, especially at primary voltages and higher because of the voltage gradiant that exists. Now you have step potential, that is, where your feet are, each could be at two substantially different potentials (or voltages) and that difference in potential could have lethal consequnces with the currents that could flow into and out of the body.
2/13/2019 5:12:52 PM EDT
[#42]
Quoted:

Thanks for that vid.

14 mins in was especially interesting about not grounding generators or solar arrays.
View Quote
There's a much longer one that's over an hour and a half.  I learned that I don't know jack about grounding and that there is a significant risk to grounding, not just more-is-better risk mitigation.

Quoted:

In what way?

I have personally done this test with a ground rod driven in fairly wet black soil, and there wasn't enough current to trip a standard breaker. Now that I think about it, there wasn't enough current to even measure on my Fluke clamp on....which does not read into the mA.

Admittedly, I haven't tried it with a GFCI breaker.

Are you saying that it would not produce any current at all?
View Quote
Uh...  It sounds like I mistook your previous comment.  According to Mike Holt, you won't trip a breaker and you won't trip a GFCI.
2/13/2019 5:16:09 PM EDT
[#43]
Quoted:
OP, in a similar manor, say a line falls from the pole. A live line on the ground will not trip any fuses or breakers as the current flow, while signifigant for danger is not enough to likely ever open a safety device like a fuse or breaker. What happens is a ground fault as I alluded to in one of  my previous posts. These are dangerous, especially at primary voltages and higher because of the voltage gradiant that exists. Now you have step potential, that is, where your feet are, each could be at two substantially different potentials (or voltages) and that difference in potential could have lethal consequnces with the currents that could flow into and out of the body.
View Quote
Yep, I've been taught to hop away from any downed lines due to step potential.

I've seen some interesting training on bringing the workspace on a pole to the same potential as well, so that the lineman is protected in his potential envelope.  I don't climb poles (or turn wrenches, or drive a crane or anything else useful) so it was interesting but kinda in one ear and out the other.  Now I'm trying to get a better understanding of it.  But I still have no intent of climbing poles.
2/13/2019 5:16:57 PM EDT
[#44]
It will make sparks
2/13/2019 5:37:47 PM EDT
[#45]
Quote History
Quoted:

Thanks for that vid.

14 mins in was especially interesting about not grounding generators or solar arrays.
View Quote
THIS!
I'm confused.
2/13/2019 5:59:35 PM EDT
[#46]
what happens when your solar array is hit by lightening?
2/13/2019 6:01:39 PM EDT
[#47]
Quote History
Quoted:
These two answers,combined, are correct. There's not a lot of info in the OP but:
1. if a GFCI is installed it will trip immediately. If not, then
2. if a breaker or fuse is in the circuit it will trip within seconds. If not then
3. wire will produce heat, followed by smoke, followed by sparks (maybe).

In any case it will be over shortly.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Depending on there size of the wire, it will either melt the wire insulation and turn it into what is essentially a heating element until failure of the circuit or trip the breaker.
Unless it's on a GFCI, which should trip.

So my answer is "not enough information provided".
These two answers,combined, are correct. There's not a lot of info in the OP but:
1. if a GFCI is installed it will trip immediately. If not, then
2. if a breaker or fuse is in the circuit it will trip within seconds. If not then
3. wire will produce heat, followed by smoke, followed by sparks (maybe).

In any case it will be over shortly.
Not sure if intentional
2/13/2019 6:06:26 PM EDT
[#48]
Quote History
Quoted:
what happens when your solar array is hit by lightening?
View Quote
I'm not sure I understand your question.  Do you mean if the solar array sustains a direct hit of some kind?
2/13/2019 6:15:45 PM EDT
[#49]
Quote History
Quoted:
what happens when your solar array is hit by lightening?
View Quote
It's fucked.
2/13/2019 6:35:07 PM EDT
[#50]
Quote History
Quoted:
what happens when your solar array is hit by lightening?
View Quote
Did you watch the long version?

I thought it was interesting that the risk of current going UP the ground rod into the equipment was a bigger problem than needing to dump excess current off the equipment inside the building.

But you're exactly right, if you isolate the solar panel from the potential current (uh, not sure how to rephrase that) that could go 'backwards' from a lightning strike pushing current up the ground rod, what happens when it takes a direct hit?  You've introduced a ton of energy, what happens to it?