8/9/2016 4:09:33 PM EDT
I have a Trane A/C system I am installing.  I just need to run the copper so I can get it charged.
Are the diameters of the two lines standard?
I don't want to make two trips to the A/C place, and it would be an easier visit if I had a clue what I was asking for.
The stubs on the existing units are 3/4"od and .37"od.
Thanks!
.
8/9/2016 6:45:10 PM EDT
[#1]
Find the installation instructions for the model you want.
Required size tables should be in there.

It depends on unit size, evaporator match, and run length.

There are some other conditions that also affect the run but they are not all that common.
8/9/2016 6:55:28 PM EDT
[#2]
and install a suction line filter while you're at it...........

Hit the edit button trying to quote you, sorry.

~ZW17


8/9/2016 6:59:00 PM EDT
[#3]
3/4 x 3/8

Pretty standard for Trane up to 3.5ton systems.

What tonage are you using?
8/9/2016 7:01:41 PM EDT
[#4]
Quote History
Quoted:
and install a suction line filter while you're at it...........

View Quote

Liquid line.

Suction line filters break down over time. They are good for about a month for a system clean up and then need to be removed.

Liquid line filters are good for the life of the system.
8/9/2016 7:23:04 PM EDT
[#5]
Add a LL drier.

I'd like to see your braze joints
8/9/2016 7:27:19 PM EDT
[#6]
Quote History
Quoted:
Add a LL drier.

I'd like to see your braze joints
View Quote



Ha. I can braze.
A friend who does this stuff for a living gave me a "new" system he pulled out of a house.
I'd like to get it installed so he can just come out and get it going with minimal effort on his part.
I'm trying to forget I have gauges and have done auto a/c....
It's a 3 ton.
8/9/2016 7:29:32 PM EDT
[#7]
Remember.  REF copper is measured OD  not ID like the plumbers use
8/9/2016 7:35:25 PM EDT
[#8]
Quote History
Quoted:
Remember.  REF copper is measured OD  not ID like the plumbers use
View Quote


This. Add an 1/8" to ID. 3/4 = 7/8. 1/4 = 3/8.

As said above, line size is dependent on length of run and unit size.

You should purge your lines with nitrogen while you burn also. Pressure test with nitrogen, release all but a pound or two of pressure, then pull vacuum. The remaining nitrogen will help displace moisture.
8/9/2016 8:02:22 PM EDT
[#9]
Quote History
Quoted:


This. Add an 1/8" to ID. 3/4 = 7/8. 1/4 = 3/8.

As said above, line size is dependent on length of run and unit size.

You should purge your lines with nitrogen while you burn also. Pressure test with nitrogen, release all but a pound or two of pressure, then pull vacuum. The remaining nitrogen will help displace moisture.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Remember.  REF copper is measured OD  not ID like the plumbers use


This. Add an 1/8" to ID. 3/4 = 7/8. 1/4 = 3/8.

As said above, line size is dependent on length of run and unit size.

You should purge your lines with nitrogen while you burn also. Pressure test with nitrogen, release all but a pound or two of pressure, then pull vacuum. The remaining nitrogen will help displace moisture.



Agree with you and then I disagree with you.  There is 3/4 OD pipe. Used in AC systems.  Refrigeration systems are 3/8 1/2 5/8 7/8 1-1/8 1-3/8 1-5/8 2-1/8 2-5/8 3-1/8 3-5/8 4-1/8 etc
8/10/2016 6:37:00 AM EDT
[#10]
Quote History
Quoted:



Agree with you and then I disagree with you.  There is 3/4 OD pipe. Used in AC systems.  Refrigeration systems are 3/8 1/2 5/8 7/8 1-1/8 1-3/8 1-5/8 2-1/8 2-5/8 3-1/8 3-5/8 4-1/8 etc
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Remember.  REF copper is measured OD  not ID like the plumbers use


This. Add an 1/8" to ID. 3/4 = 7/8. 1/4 = 3/8.

As said above, line size is dependent on length of run and unit size.

You should purge your lines with nitrogen while you burn also. Pressure test with nitrogen, release all but a pound or two of pressure, then pull vacuum. The remaining nitrogen will help displace moisture.



Agree with you and then I disagree with you.  There is 3/4 OD pipe. Used in AC systems.  Refrigeration systems are 3/8 1/2 5/8 7/8 1-1/8 1-3/8 1-5/8 2-1/8 2-5/8 3-1/8 3-5/8 4-1/8 etc


Of course there is. OP specifically said 3/4, I used that as an example. I recently put in a VRF system that used every size made 2-5/8 and smaller.
8/10/2016 6:52:06 AM EDT
[#11]
Need the model numbers to be sure but 3 to. R410a systems are normally 3/4 and 3/8. Don't forget use dry nitrogen when soldering and to use 5% silver solder.
8/10/2016 1:13:17 PM EDT
[#12]
Quote History
Quoted:

Liquid line.

Suction line filters break down over time. They are good for about a month for a system clean up and then need to be removed.

Liquid line filters are good for the life of the system.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
and install a suction line filter while you're at it...........


Liquid line.

Suction line filters break down over time. They are good for about a month for a system clean up and then need to be removed.

Liquid line filters are good for the life of the system.

8/10/2016 2:28:24 PM EDT
[#13]
Quote History
Quoted:
Need the model numbers to be sure but 3 to. R410a systems are normally 3/4 and 3/8. Don't forget use dry nitrogen when soldering and to use 5% silver solder.
View Quote


Brazing.