What is the minimum size EMT to hold 3 #2's, 3 # 10's, and a #6 ground? All wire is THHN. I'm too lazy to dig out my code book. Thanks.
Link Posted: 10/17/2001 6:25:06 PM EDT
[#1]
How long a run?
Link Posted: 10/17/2001 6:28:33 PM EDT
[#2]
Don't matter. Take the sum of the cross section of the conductors, and look up the allowable fill of the conduit, in sq. inches. That will be on a chart in the cook book.
Link Posted: 10/17/2001 6:31:49 PM EDT
[#3]
Ahh what I'm saying is it isn't a 2' or shorter nipple where 60% fill can be used.  Nippple nipple nipple...did I say ni......
Link Posted: 10/17/2001 6:32:55 PM EDT
[#4]
Ive had toooooooo many beers to figure conduitfill do it your self   1 1/4 inch should cover.
Link Posted: 10/17/2001 6:34:04 PM EDT
[#5]
My guess is 1 1/4.


toooo (beaten by the iceman)
Link Posted: 10/17/2001 6:52:34 PM EDT
[#6]
Nope, no nipple. 1 1/4 was my guess, but I'll do the damn math. Thanks anyway.