Posted: 9/2/2015 8:31:39 PM EDT
Issue solved, thanks for all the help!!!
Link Posted: 9/2/2015 8:36:07 PM EDT
[#1]


Why do you need all three? 21 year hvac svc tech here.

Link Posted: 9/2/2015 8:43:03 PM EDT
[#2]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Why do you need all three? 21 year hvac svc tech here.


View Quote


This.  

How do you know those parts are bad?

Also, if its locking out on roll-out you may very well have a cracked heat exchanger.
Link Posted: 9/2/2015 8:47:06 PM EDT
[#3]


Discussion ForumsJump to Quoted PostQuote History
Quoted:
This.



How do you know those parts are bad?



Also, if its locking out on roll-out you may very well have a cracked heat exchanger.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:

Why do you need all three? 21 year hvac svc tech here.









This.



How do you know those parts are bad?



Also, if its locking out on roll-out you may very well have a cracked heat exchanger.


I'm seeing it as a gaspack with and induced draft setup. Probably a bad ignitor or induced draft motor.
Link Posted: 9/2/2015 8:52:25 PM EDT
[#4]
Discussion ForumsJump to Quoted PostQuote History
Quoted:

I'm seeing it as a gaspack with and induced draft setup. Probably a bad ignitor or induced draft motor.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Why do you need all three? 21 year hvac svc tech here.




This.

How do you know those parts are bad?

Also, if its locking out on roll-out you may very well have a cracked heat exchanger.

I'm seeing it as a gaspack with and induced draft setup. Probably a bad ignitor or induced draft motor.


Really just need the pressure switch. This winter it would run fine then stop producing heat, but the fan kept running and would not shut off blowing. Pulling the main breaker reset the unit and it would heat again. The coil is clean, and the filters were clean. Also no obstructions in the duct work. Figured I would replace the other parts while I was in there, ( probably not necessary)

Thanks for all the questions!
Link Posted: 9/2/2015 8:56:56 PM EDT
[#5]
Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?
Link Posted: 9/2/2015 8:57:28 PM EDT
[#6]
Looks like its new heater time
Link Posted: 9/2/2015 8:59:51 PM EDT
[#7]

Discussion ForumsJump to Quoted PostQuote History
Quoted:


Looks like its new heater time
View Quote
I wish all my customers had your attitude.

 
Link Posted: 9/2/2015 9:09:00 PM EDT
[#8]
The unit is made by Armstrong, I've sold this brand for the last 25 yrs for the distributor I work for.
Link Posted: 9/2/2015 9:16:28 PM EDT
[#9]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?
View Quote


Correct, the blower motor is running. So, its the pressure switch?
Link Posted: 9/2/2015 9:17:53 PM EDT
[#10]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Looks like its new heater time
View Quote

It really is, I know. But need to make it till next spring.
Link Posted: 9/2/2015 9:19:47 PM EDT
[#11]

Discussion ForumsJump to Quoted PostQuote History
Quoted:
Correct, the blower motor is running. So, its the pressure switch?

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:

Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?




Correct, the blower motor is running. So, its the pressure switch?

Read my post again.  It sounds like the limit. i know how I'd check it.  Do you own a meter?

 
Link Posted: 9/2/2015 9:22:08 PM EDT
[#12]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Correct, the blower motor is running. So, its the pressure switch?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?


Correct, the blower motor is running. So, its the pressure switch?

Use a multimeter to check for voltage on each terminal of the pressure switch. Check each one to ground or back to the mistral of the transformer.  If you only have voltage on one terminal the switch is not closed.
The presses switch can be replaced with a generic
Link Posted: 9/2/2015 9:25:07 PM EDT
[#13]


Discussion ForumsJump to Quoted PostQuote History
Quoted:
Use a multimeter to check for voltage on each terminal of the pressure switch. Check each one to ground or back to the mistral of the transformer.  If you only have voltage on one terminal the switch is not closed.


The presses switch can be replaced with a generic
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:





Quoted:




Quoted:


Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?






Correct, the blower motor is running. So, its the pressure switch?





Use a multimeter to check for voltage on each terminal of the pressure switch. Check each one to ground or back to the mistral of the transformer.  If you only have voltage on one terminal the switch is not closed.


The presses switch can be replaced with a generic
Of the same temp rating.



On edit , I read temp switch. Carry on.
Link Posted: 9/2/2015 9:27:31 PM EDT
[#14]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Of the same temp rating.

On edit , I read temp switch. Carry on.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Quoted:
Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?


Correct, the blower motor is running. So, its the pressure switch?

Use a multimeter to check for voltage on each terminal of the pressure switch. Check each one to ground or back to the mistral of the transformer.  If you only have voltage on one terminal the switch is not closed.
The presses switch can be replaced with a generic
Of the same temp rating.

On edit , I read temp switch. Carry on.


I don't have a multimeter, but am willing to just replace the parts.
Link Posted: 9/2/2015 9:28:44 PM EDT
[#15]

Discussion ForumsJump to Quoted PostQuote History
Quoted:
I don't have a multimeter, but am willing to just replace the parts.

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:


Quoted:


Quoted:


Quoted:

Sounds more like a bad limit. The pressure switch is to ensure the induced draft motor is working.  When you say fan is running, You mean the blower motor not the small induced draft motor, correct?




Correct, the blower motor is running. So, its the pressure switch?



Use a multimeter to check for voltage on each terminal of the pressure switch. Check each one to ground or back to the mistral of the transformer.  If you only have voltage on one terminal the switch is not closed.

The presses switch can be replaced with a generic
Of the same temp rating.



On edit , I read temp switch. Carry on.





I don't have a multimeter, but am willing to just replace the parts.

Then by all means, please call a repair guy. This is a gas heater that will kill you if it isnt working correctly.

 
Link Posted: 9/2/2015 9:29:35 PM EDT
[#16]
that is a 165 degree limit.if it has been getting that hot and locking out,  it will run indoor fan constantly.
heat exchanger needs to be looked at by  professional for your safety.
Link Posted: 9/2/2015 9:38:07 PM EDT
[#17]

Discussion ForumsJump to Quoted PostQuote History
Quoted:



I wish all my customers had your attitude.  
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:

Looks like its new heater time
I wish all my customers had your attitude.  
I do installs
Link Posted: 9/2/2015 9:40:59 PM EDT
[#18]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
that is a 165 degree limit.if it has been getting that hot and locking out,  it will run indoor fan constantly.
heat exchanger needs to be looked at by  professional for your safety.
View Quote


Thanks for the help!

Link Posted: 9/2/2015 9:41:02 PM EDT
[#19]

Discussion ForumsJump to Quoted PostQuote History
Quoted:



I do installs
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:


Quoted:

Looks like its new heater time
I wish all my customers had your attitude.  
I do installs


Link Posted: 9/2/2015 9:43:55 PM EDT
[#20]
I would get a tech to check the heat exchanger before winter gets here. With the age of the unit it is possible to have a rust hole or crack, I see several a year out of this series that need replaced.
Link Posted: 9/2/2015 10:02:07 PM EDT
[#21]
Quoted:
Issue solved, thanks for all the help!!!
View Quote

Good, I guess. You erasing the original post has certainly helped those of us who would have like to learn something here.

Thanks again.
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top