I need a new HVAC - 4 ton split system.

Current system is 20 years old, installed with the house.  In getting quotes, one of my guys says he will reuse the existing lineset.

The previous system is R22, the new will be R410 of course.

Does this matter?
Link Posted: 6/15/2016 8:17:33 PM EDT
[#1]
Bump...

Not a HVAC guy but I would replace the lines.  Different oils etc..  I'm not certain if a good nitrogen purge and 500 micron vacuum would clean the old oils.

The HVAC guys will be along soon...  Looking forward to their response and learning something.
Link Posted: 6/15/2016 8:35:41 PM EDT
[#2]
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.
Link Posted: 6/15/2016 8:36:44 PM EDT
[#3]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.
View Quote



What if it is 80 feet of line and two stories, and down a brick wall?
Link Posted: 6/15/2016 8:44:09 PM EDT
[#4]
I worked in a townhouse that the line set was built into a load bearing wall and like 70 feet long.

the labor to remove it would have been rediculous.

it was Re used.

I say it's fine but  if it is easy to get to and my house I'm replacing It
Link Posted: 6/15/2016 8:50:39 PM EDT
[#5]
If they are the right size they can be reused.  

Not an HVAC guy but I work in the apartment industry and we are dealing with this industry wide across the country.
Link Posted: 6/16/2016 10:53:42 AM EDT
[#6]


Discussion ForumsJump to Quoted PostQuote History
Quoted:
What if it is 80 feet of line and two stories, and down a brick wall?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:





Quoted:


Replace the lines.


The process to clean them out for the different lubricant is not worth the time., effort, or chance.

What if it is 80 feet of line and two stories, and down a brick wall?



If it is rather easy and practical to do so, sure, go ahead and replace it.  Depending on if you are increasing/decreasing sizes, the diameters of the lineset (especially the suction line) may change.  Typically, the liquid line (the smaller one) is usually 3/8", but the larger (suction) line will vary depending on the size of the unit.  Sometimes I've seen where contractors who are re-using the lineset have to match up the new units size to the old suction line and there's a 1/8" difference.  There's usually no harm in this, but anything more than 1/8" can be looking for trouble to start down the road.



Also what I mean by "easy", is the lineset on the outside of the exterior wall?  When it goes into the home, would it be easy to gain access to braze the joint where the lines would meet?  For my own house, the lineset is actually inside the wall so I'll be re-using that thing for quite a while.





 
Link Posted: 6/16/2016 11:03:36 AM EDT
[#7]
Discussion ForumsJump to Quoted PostQuote History
Quoted:



What if it is 80 feet of line and two stories, and down a brick wall?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.



What if it is 80 feet of line and two stories, and down a brick wall?



What size are your current lines?


Link Posted: 6/16/2016 11:30:56 AM EDT
[#8]
Discussion ForumsJump to Quoted PostQuote History
Quoted:



What if it is 80 feet of line and two stories, and down a brick wall?
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.



What if it is 80 feet of line and two stories, and down a brick wall?


When the new system fails early and the warranty is voided you can save again.
Link Posted: 6/16/2016 1:36:34 PM EDT
[#9]

Discussion ForumsJump to Quoted PostQuote History
Quoted:
What size are your current lines?





http://i63.tinypic.com/ie1kxc.jpg
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:


Quoted:

Replace the lines.

The process to clean them out for the different lubricant is not worth the time., effort, or chance.






What if it is 80 feet of line and two stories, and down a brick wall?






What size are your current lines?





http://i63.tinypic.com/ie1kxc.jpg


That's a good rough guide, however each manufacturer has different specs for their units.  OP needs to use the specs for the new unit he wants and compare to existing lineset.



 
Link Posted: 6/16/2016 5:25:39 PM EDT
[#10]
Discussion ForumsJump to Quoted PostQuote History
Quoted:

That's a good rough guide, however each manufacturer has different specs for their units.  OP needs to use the specs for the new unit he wants and compare to existing lineset.
 
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Quoted:
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.



What if it is 80 feet of line and two stories, and down a brick wall?



What size are your current lines?


http://i63.tinypic.com/ie1kxc.jpg

That's a good rough guide, however each manufacturer has different specs for their units.  OP needs to use the specs for the new unit he wants and compare to existing lineset.
 

And then figure out what he is going to do with the contaminated solvent.
Link Posted: 6/16/2016 8:27:33 PM EDT
[#11]
Replace. If your spending that kind of money a lineset is cheap. Especially since your getting a new A coil and condensing unit. Be smart and stop trying to cut corners.
Link Posted: 6/16/2016 8:54:56 PM EDT
[#12]
it depends, what size do you have and what brand, model are you installing? go by the manufactures specs.



you must maintain a certain velocity in order to have proper oil return to the compress or your bearings in the compressor will run dry
Link Posted: 6/17/2016 9:21:21 AM EDT
[#13]

Discussion ForumsJump to Quoted PostQuote History
Quoted:



And then figure out what he is going to do with the contaminated solvent.
View Quote


Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.



 
Link Posted: 6/17/2016 1:28:15 PM EDT
[#14]
Discussion ForumsJump to Quoted PostQuote History
Quoted:

Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.
 
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:

And then figure out what he is going to do with the contaminated solvent.

Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.
 


The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.
Link Posted: 6/17/2016 8:48:24 PM EDT
[#15]
Being in the HVAC trade if it was my house I would replace the line set. It is cheap insurance

R22 and R410A oils are different, and when R22(mineral) oil mixes with the R410A(POE) oil the oil become acidic and gums up. So 2 things start happening the acid starts eating away at the compressor windings, and you dont get the proper lube to the compressor.

So if you would like to replace a compressor in a few years reuse the lineset.
Link Posted: 6/17/2016 10:24:33 PM EDT
[#16]
So RX-11 doesn't do what it says?
Link Posted: 6/19/2016 2:33:13 PM EDT
[#17]

Discussion ForumsJump to Quoted PostQuote History
Quoted:
The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:



Quoted:


Quoted:



And then figure out what he is going to do with the contaminated solvent.


Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.

 




The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.


The RX-11 flush needs to be completely evacuated from the lineset before any sort of new refrigerant is added.  



 
Link Posted: 6/19/2016 4:02:19 PM EDT
[#18]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:

And then figure out what he is going to do with the contaminated solvent.

Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.
 


The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.


You just dump that shit in the yard.  I have plenty of places I need roundup  
Link Posted: 6/19/2016 8:09:16 PM EDT
[#19]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


You just dump that shit in the yard.  I have plenty of places I need roundup  
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Quoted:

And then figure out what he is going to do with the contaminated solvent.

Uh, if there's some kind of 'contaminated solvent' in the lineset once you get the system installed and filled with refrigerant, you've got bigger problems coming than properly sizing the lineset.
 


The contaminated solvent will be in the bucket you pumped it into when cleaning the lineset.


You just dump that shit in the yard.  I have plenty of places I need roundup  


YOU may get away tith that.

Folks that have a license, insurance, etc.  may not be so cavalier.
Link Posted: 6/19/2016 10:34:36 PM EDT
[#20]
I have personally watched more licensed pros vent R22 into the air than you'd imagine.  I cannot imagine a little solvent would be any different.
Link Posted: 6/19/2016 10:39:30 PM EDT
[#21]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


When the new system fails early and the warranty is voided you can save again.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Replace the lines.
The process to clean them out for the different lubricant is not worth the time., effort, or chance.



What if it is 80 feet of line and two stories, and down a brick wall?


When the new system fails early and the warranty is voided you can save again.


Which manufacturer voids the warranty because a lineset was reused?   Not Trane, not American standard, not carrier, not Goodman.  So far, they have guidance to the installer on sizing and purging from what I have found.

Three quotes so far in the past three days, all from highly recommended shops, and thus far all have stated they will reuse the lineset.  One told me nitrogen purge.  One said solvent then nitrogen.  The other said he purges with a puron flush.
Link Posted: 6/20/2016 1:01:01 AM EDT
[#22]
Unless it is a HUGE pain in the ass, my shop would recommend changing the line set, and if it were my house I would too.
Link Posted: 6/20/2016 12:06:00 PM EDT
[#23]
Which manufacturer voids the warranty because a lineset was reused?
View Quote


None automatically.
If they decide to inspect and find it was not cleaned properly they can.
Link Posted: 6/20/2016 3:40:01 PM EDT
[#24]
I'm looking at replacing my unit on a two story house. A/C guy insists
on using new lines, stating there could be any number of things wrong

with the old ones.  That thought, along with the things guys pointed out

above make me think he is right.




He will run the lines up the wall to the attic through a fake down spout.

I'm not over joyed about that but it will look better than a line set

running up to the attic.






Link Posted: 6/20/2016 8:19:19 PM EDT
[#25]
Link Posted: 6/20/2016 8:51:45 PM EDT
[#26]

Discussion ForumsJump to Quoted PostQuote History
Quoted:


Replace the lineset, it's the right thing to do.



I'm not going to type out a long drawn out response about why RX11 flush is snake oil, buts it's pretty much snake oil unless you use a few gallons of it, in which case you just bought a new lineset twice over.



What's 75' of lineset up a wall going to add to the job? $500-$750 to a $10k job?



This is not the area where you want to pinch pennies.
View Quote


If I remember right, most techs these days use a nitrogen purge and subsequently pull vacuum to evacuate the lines instead of that RX11 crap.  Is that about right for reusing a lineset?



 
Link Posted: 6/20/2016 9:09:17 PM EDT
[#27]
Link Posted: 6/20/2016 9:24:31 PM EDT
[#28]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Now manufacturers are saying that the mixing of oils in small quantities doesn't hurt anything.  

Who knows? I have always just replaced the lineset.


View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Originally Posted By Texas smooth:
Quoted:
Replace the leanest, it's the right thing to do.

I'm not going to type out a long drawn out response about why RX11 flush is snake oil, buts it's pretty much snake oil unless you use a few gallons of it, in which case you just bought a new leanest twice over.

What's 75' of lineset up a wall going to add to the job? $500-$750 to a $10k job?

This is not the area where you want to pinch pennies.

If I remember right, most techs these days use a nitrogen purge and subsequently pull vacuum to evacuate the lines instead of that RX11 crap.  Is that about right for reusing a lineset?
 


Now manufacturers are saying that the mixing of oils in small quantities doesn't hurt anything.  

Who knows? I have always just replaced the lineset.




NVM. Stupid question
Link Posted: 6/21/2016 3:59:31 PM EDT
[#29]
Discussion ForumsJump to Quoted PostQuote History
Quoted:


Now manufacturers are saying that the mixing of oils in small quantities doesn't hurt anything.  

Who knows? I have always just replaced the lineset.




View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
Quoted:
Replace the lineset, it's the right thing to do.

I'm not going to type out a long drawn out response about why RX11 flush is snake oil, buts it's pretty much snake oil unless you use a few gallons of it, in which case you just bought a new lineset twice over.

What's 75' of lineset up a wall going to add to the job? $500-$750 to a $10k job?

This is not the area where you want to pinch pennies.

If I remember right, most techs these days use a nitrogen purge and subsequently pull vacuum to evacuate the lines instead of that RX11 crap.  Is that about right for reusing a lineset?
 


Now manufacturers are saying that the mixing of oils in small quantities doesn't hurt anything.  

Who knows? I have always just replaced the lineset.






Short of something in writing not worth it.

When they have to pay $$ watch what they say.
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top