What is the minimum size EMT to hold 3 #2's, 3 # 10's, and a #6 ground? All wire is THHN. I'm too lazy to dig out my code book. Thanks.
Link Posted: 10/17/2001 5:25:06 PM EST
How long a run?
Link Posted: 10/17/2001 5:28:33 PM EST
Don't matter. Take the sum of the cross section of the conductors, and look up the allowable fill of the conduit, in sq. inches. That will be on a chart in the cook book.
Link Posted: 10/17/2001 5:31:49 PM EST
Ahh what I'm saying is it isn't a 2' or shorter nipple where 60% fill can be used. Nippple nipple nipple...did I say ni......
Link Posted: 10/17/2001 5:32:55 PM EST
Ive had toooooooo many beers to figure conduitfill do it your self 1 1/4 inch should cover.
Link Posted: 10/17/2001 5:34:04 PM EST
[Last Edit: 10/17/2001 5:31:52 PM EST by Nekkid80]
My guess is 1 1/4. toooo (beaten by the iceman)
Link Posted: 10/17/2001 5:52:34 PM EST
Nope, no nipple. 1 1/4 was my guess, but I'll do the damn math. Thanks anyway.