Can't you share a neutral as long as the breakers for the shared circuits are tied together? Or is that something different?
View Quote
That is a multi-wire branch circuit.
The neutral only carries any imbalance between the two legs so it is (theoretically) never more than one breakers full current.
Problems occur with loads with a poor power factor and non-sinusoidal current flow that do not 'balance' correctly.
Computer power supplies (though now improved) had horrid power factors and overloaded plenty of neutrals in commercial (office) type settings.
The narrow pulses from switching style power supplies react with the inductance in the distribution wiring to cause overloading of shared neutral.
This was one of the things that drove the requirement for power factor control on PC power supplies.
You can only put two wires in the bar of a panel that is listed for that installation.
Neutrals may NEVER have two wires unless it happens to be a stranded conductor and within the allowed size range for the termination.
You can use 'adapters' to split up a larger stranded wire into multiple holes.
You cannot simply separate the stranding into multiple holes.