Posted: 9/9/2023 3:10:25 PM EST
I’m planning to retrofit my tank water heater to a Rinnai tankless condensing unit (180k BTU)

My furnace (assuming 80k BTU, need to confirm) has 2” PVC inlet and exhaust vents. I’d like to locate the water heater in the same room sharing the existing vents. I know you can vent multiple tankless heaters on a common vent, but looking for the code section for venting with a furnace. I’m in SC specifically.

ETA:   According to installation instructions, you can’t common vent with a non-Rinnai tankless heater.
Hydra
Link Posted: 9/10/2023 9:38:25 PM EST
[#1]
Definitely not on a 2" PVC run.

The tankless I've always installed (Takagi, usually 199k BTU units) require 3" venting for 70' runs or less, and 4" PVC for runs up to 100'. ALL common venting requires at LEAST a 4" PVC pipe run.

I'm not hip to Rinnai but physics is physics so I'd say that's going to be a hard no.
Link Posted: 9/28/2023 9:08:08 PM EST
[#2]
I know when I looked at the our code, it has to be a Y-pipe and a non-reversing baffle is required in the past, but it is no longer allowed in new installations/constructions.

Finding a non-reversing Y-pipe is nigh-impossible these days unless its custom made
Link Posted: 10/9/2023 11:41:17 AM EST
[#3]
You would like to, but you can’t. No building code or manufacturer is going to allow that.
Link Posted: 10/9/2023 11:48:37 AM EST
[#4]
The problem is you need to make it 100% certain that your forced vent furnace won't blow exhaust backwards through your water heater into living space, and your WH can't blow exhaust through the furnace.

Previously the code allowed one way valves in the flue, now the code eliminates that possible (and deadly) failure point by saying no shared flue.
Link Posted: 11/1/2023 4:35:17 PM EST
[#5]
Just an FYI update… in SC you can common vent exhaust flues with Condensing furnaces and tankless water heaters in accordance with manufacturer’s guidelines. In my case a Lennox furnace and Navien tankless water heater.
Link Posted: 11/2/2023 4:19:26 PM EST
[#6]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Just an FYI update… in SC you can common vent exhaust flues with Condensing furnaces and tankless water heaters in accordance with manufacturer’s guidelines. In my case a Lennox furnace and Navien tankless water heater.
View Quote


That’s cool, but both manufacturers say no. Navien can be common vented with other Naviens when they’re tied together on the control system.
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top