mike,
Quoted:
I recently purchased a 7000 watt Coleman Powermate generator. I would like to be set up with transfer switch but do not know which to get? I plan on eventually getting a larger propane powered generator, 15-20,000 watts. Should I get one for the 7,000 watt generator or go ahead and put in one large enough to handle the home generator? What are some good name brands?
to clarify one thing –– there are two types of transfer switches: whole-house and load side.
a whole-house transfer switch does just what it sounds like it does. in place of the service drop from the utility company, the generator supplies power to the main breaker panel. now then, whether or not the generator can actually provide power *concurrently* to all of the circuits is another matter. but a whole-house transfer switch will be rated for (at minimum) your service drop ampacity (typically 100A, 150A, or 200A –– and in some cases greater). in some older houses it may be 60A, but you rarely see residential service that small these days. powering your entire house from a generator is generally impractical, as you need a giant genset and it will, in turn, suck down fuel (for this size, it will be diesel, propane, or natural gas). note that the installation of a whole house transfer switch is usually a "big deal" as far as an electrician is concerned, because there is usually no convenient way to (easily) turn off the power on the feed side. so, a call to the utility company is very much necessary, to have a guy/crew come out and disconnect the feed to the house at the pole. this can get interesting/expensive.
a load side transfer switch is more common, but has limitations. a load side transfer switch allows you to select individual branch circuits to power with your generator. for example, you may decide you need to provide generator power to your refrigerator, furnace blower motor, and a couple of lights. you then install the transfer switch adjacent to the main breaker panel, and rewire those circuits (and only those circuits) such that depending on a switch setting they are powered by the utility company or the generator. these types of transfer switches can get fairly comprehensive –– 10 circuits is not uncommon. in fact, you may find that 10 circuits covers 99.99% of all of the stuff you need to power when the utility power is off. note that installation of a load side transfer switch is not a big deal to an electrician. no special measures with the utility company are necessary.
finally, there is a wholly separate method of powering your entire main breaker panel from a generator, and that involves a backfeed breaker used in conjunction with a lockout plate. your generator attaches to the backfeed breaker, and the lockout plate moves in such a manner that either the utility company is supplying power or the generator is supplying power –– and in no case are both! again, no special measures with the utility company are necessary for this approach. the primary benefit of this approach is that you don't have to decide during installation what branch circuits should be powered by the generator.
Quoted:
Also, I need to run a water pump and need 220V. How can I do this with my generator? It only has 4 120 and a 240 outlet.
all residential power in the US is 120/240Vac split phase. the utility company provides this power using three wires, L1, L2, and N. from L1 to L2 is 240Vac, and both L1 to N and L2 to N are both 120Vac.
your main breaker box is wired such that the 120Vac loads are "mostly" evenly spread across the L1 and L2 busses, using single width circuit breakers. a black wire from the breaker is paired up with a white wire landed on the neutral bar to serve 120Vac branch circuits. but 240Vac loads like your water pump use a "wide" double pole breaker which straddles both L1 and L2 –– here a black and a red wire come off the double pole breaker, plus a neutral is landed on the neutral bar.
it sounds like your current generator has a pair of duplex 120Vac outlets, and most likely a single 240Vac 30A outlet. you would need to buy or construct a cable assembly which will go from the 240Vac 30A outlet to the transfer switch. the water pump will utilize a double pole breaker on the transfer switch for power. see the first two positions in the image i attached below, and note how their handles are tied together.
if you are planning on upgrading to a much larger generator in the near future, you should simply install the larger capacity transfer switch or whole house transfer switch. there is no point in paying for an upsized transfer switch, plus paying the electrician yet again to wire it in.
ar-jedi
here is an example 10 circuit 50A transfer switch
http://reliancecontrols.com/ProductDetail.aspx?Q510CE