  • Joined Apr 2007
  • Posts 1143
  • EE 0% (0)
USA WV, USA
Posted: 12/14/2010 8:10:57 AM EST
I have been renting a house for a few months and last night the thermostat said 59 but was set a 70 and the house was cold. Its an old house but has new windows and is mostly insulated. The Furnace is gas and is in the basement which is not heated. The thermostat is a Honeywell digital and the heat kick on about every 7 minutes and runs for around 3 minutes and repeats the cycle, The air coming from the vents is warm but it is not heating up the house. This has not been a problem until the outside tempeture went below 20. Any help, suggestions, or experience is greatly appreciated.

Thanks
"Those who would give up liberty for the sake of security deserve neither liberty nor security."
Member
Avatar
Bronze
Offline
  • Joined Mar 2008
  • Posts 2432
  • EE 100% (3)
USA TX, USA
Link Posted: 12/14/2010 8:12:50 AM EST
Just breath deep. It will all be over soon. Now go to sleep.

Turn out the lights, the party's over.............
Avatar
Bronze
Offline
  • Joined Oct 2004
  • Posts 23645
  • EE 0% (0)
USA AL, USA
Link Posted: 12/14/2010 8:13:26 AM EST
I would call the landlord.
"It's my job to have kids, Mr. Mayor, and your job to take care of them." -welfare mother, screaming at then NYC mayor John Lindsay- The Myth of the Working Poor by Steve Malanga
Some men...you just can't reach
Avatar
Bronze
Offline
  • Joined Nov 2008
  • Posts 3894
  • EE 100% (2)
USA TX, USA
Military
Link Posted: 12/14/2010 8:14:17 AM EST
[Last Edit: 12/14/2010 8:15:03 AM EST by skunk-ape]
don't screw with it.. call the landlord.. it is his problem
If you mess with it first... they could blame you


ETA: and go buy at least one Carbon Monoxide Detector NOW
even if you have to pay out of your pocket, just do it.


Now remember, things look bad and it looks like you're not gonna make it, then you gotta get mean.
I mean plumb, mad-dog mean. Cause if you lose your head and you give up then you neither live nor win. That's just the way it is.
Just some dude
Avatar
Bronze
Offline
  • Joined Mar 2007
  • Posts 12566
  • EE 100% (9)
USA OR, USA
Link Posted: 12/14/2010 8:14:18 AM EST

Originally Posted By callgood:
I would call the landlord.

+1. One of the benefits of renting.
Don't let anybody else grind your pepper, chop your garlic or squeeze your lemons.

You learn something new every day whether you like it or not.
Member
Avatar
Bronze
Offline
  • Joined Apr 2007
  • Posts 1144
  • EE 0% (0)
USA WV, USA
Link Posted: 12/14/2010 8:14:41 AM EST
Yeah right, the landlord is a joke and is actually in Floridia right now.
Originally Posted By callgood:
I would call the landlord.


"Those who would give up liberty for the sake of security deserve neither liberty nor security."
Member
Avatar
Bronze
Offline
  • Joined Jun 2009
  • Posts 1314
  • EE 0% (0)
USA FL, USA
Link Posted: 12/14/2010 8:19:36 AM EST
if gas forced air it is mostlikely triping off on a highlimit temp sensor ,try finding intake airfilters and replace to insure good airflow,also the antisipator setting on the digital t stat might need to be changed for a highgher run time,also a heat vent might be too close to the t stat heating it up before the house, so close that one down, good luck

Basic
Offline
  • Joined Oct 2004
  • Posts 663
  • EE 0% (0)
USA IL, USA
Link Posted: 12/14/2010 8:26:40 AM EST
IF calling the landlord doesn't help, clean the flame sensor with fine sandpaper. It's probably dirty and sending a false signal.

Member
Avatar
Bronze
Offline
  • Joined Nov 2009
  • Posts 382
  • EE 0% (0)
USA VA, USA
Link Posted: 12/14/2010 8:36:35 AM EST
Originally Posted By CRNUMBER:
IF calling the landlord doesn't help, clean the flame sensor with fine sandpaper. It's probably dirty and sending a false signal.


had to do this last week

Basic
Offline
  • Joined May 2005
  • Posts 714
  • EE 100% (91)
USA OH, USA
Link Posted: 12/14/2010 8:44:21 AM EST
Originally Posted By CRNUMBER:
IF calling the landlord doesn't help, clean the flame sensor with fine sandpaper. It's probably dirty and sending a false signal.


That. Your furnace is short cycling. There are a number of possible causes (Google "furnace short cycles"), but the flame sensor is a likely, quick, and easy place to start. I've had to lightly sand my flame sensor a couple times in the last 10 years.

Last year my furnace started short cycling. It turns out that the old (1950s-era) mechanical thermostat (on the wall) went bad. I replaced it with a cheap digital one.


Basic
Offline
  • Joined Jun 2010
  • Posts 89
  • EE 0% (0)
USA NC, USA
Link Posted: 12/14/2010 8:44:38 AM EST
Older houses often have fireplaces that are no longr used. Make sure the draft is closed up inside the fireplace. Still, if you hold a smoldering piece of paper in front of the fireplace you'll probably see the smoke sucking into the chimney. It's a common problem - fireplaces suck heat out of a house and sometimes suck more when they are in use. Cover it over with cardboard, newspaper taped in place - whatever it takes to stop air flow. Use the same smoky match or paper to check windows and doors. I recently found that my cooking stove vent was acting in reverse and artic air was literally blasting down from it into the kitchen......so I Seran wrapped over the vent.

Pavlov's deaf dog
Avatar
Gold
Offline
  • Joined May 2007
  • Posts 12455
  • EE 100% (166)
USA WI, USA
Link Posted: 12/14/2010 8:46:21 AM EST
I would call the heating and air guy and have him bill the landlord.

Probably the thermocouple.
"It's hard to kill a horse with a flute."
"If there are no dogs in heaven, then when I die I want to go where they went."
Boycotting GM. Not one dime.
LaRue customer for life!
He who needs to stop buying toys and simplify!
Avatar
Bronze
Offline
  • Joined Feb 2006
  • Posts 7331
  • EE 100% (8)
USA MO, USA
Link Posted: 12/14/2010 8:46:22 AM EST
Originally Posted By callgood:
I would call the landlord.


DING. Key word being RENTING.
"If you're not shooting you should be loading, if you're not loading you should be moving, if you're not moving, someone is gonna cut off your head and put it on a stick...." -Clint Smith, Thunder Ranch

NRA Life Member
Too stupid to know better.
Avatar
Bronze
Offline
  • Joined Jul 2010
  • Posts 236
  • EE 100% (1)
USA IN, USA
Link Posted: 12/14/2010 8:56:37 AM EST
[Last Edit: 12/14/2010 8:56:52 AM EST by proto_moose]
If it is actually lighting, it is NOT the flame sensor. Flame sensor 99.999999% of the time won't even prove ignition if it's bad.


ETA: Call landlord.

Tactical Vulpine
Avatar
Bronze
Offline
  • Joined Jun 2004
  • Posts 6638
  • EE 100% (6)
USA VA, USA
Link Posted: 12/14/2010 9:13:52 AM EST
Is the thermostat above a vent?

-Foxxz
Look at my source! My source is amazing!
Basic
Offline
  • Joined Sep 2010
  • Posts 2139
  • EE 0% (0)
USA CA, USA
Link Posted: 12/14/2010 9:15:37 AM EST
Originally Posted By grafixghost:
Yeah right, the landlord is a joke and is actually in Floridia right now.
Originally Posted By callgood:
I would call the landlord.




Then it looks like the joke's on you, son. It's his RESPONSIBILITY to unfuck the situation. And if you look at your lease agreement there should be a standard clause in there about the place being 'liveable'. That's a catch-all for working plumbing, safe electrical and gas, and not freezing your dick off in the winter.

Basic
Offline
  • Joined Apr 2001
  • Posts 835
  • EE 100% (2)
USA MN, USA
Link Posted: 12/14/2010 9:58:53 AM EST
Is there anything blocking the exhaust vents?

I just had this problem Saturday, but then again, I also had 17" of snow over the weekend.

Member
Avatar
Bronze
Offline
  • Joined Apr 2007
  • Posts 1145
  • EE 0% (0)
USA WV, USA
Link Posted: 12/14/2010 10:14:32 AM EST
Thanks for the responces.

No vent below thermostat
No vents blocked

Going to clean flame sensors and hope for the best.
"Those who would give up liberty for the sake of security deserve neither liberty nor security."
Too stupid to know better.
Avatar
Bronze
Offline
  • Joined Jul 2010
  • Posts 237
  • EE 100% (1)
USA IN, USA
Link Posted: 12/14/2010 10:19:16 AM EST
Originally Posted By powdershots:
if gas forced air it is mostlikely triping off on a highlimit temp sensor ,try finding intake airfilters and replace to insure good airflow,also the antisipator setting on the digital t stat might need to be changed for a highgher run time,also a heat vent might be too close to the t stat heating it up before the house, so close that one down, good luck


Did you check your filter? powdershots might be close on the limit idea.

JIP
Team Member
Avatar
Bronze
Offline
  • Joined Sep 2008
  • Posts 5125
  • EE 0% (0)
USA PA, USA
Link Posted: 12/14/2010 10:19:45 AM EST

Originally Posted By powdershots:
if gas forced air it is mostlikely triping off on a highlimit temp sensor ,try finding intake airfilters and replace to insure good airflow,also the antisipator setting on the digital t stat might need to be changed for a highgher run time,also a heat vent might be too close to the t stat heating it up before the house, so close that one down, good luck

This, and call the landlord I have had the same issue and I changed the filter and it fixed it. You should definitely call the landlord if there is any doubt as heating issues are nothing o take lightly ans if you are concerned he might even get you a CM detector I know in the one apartment I own I bought my tennant one plus smoke detectors.

Basic
Offline
  • Joined Jun 2008
  • Posts 1393
  • EE 0% (0)
USA IL, USA
Link Posted: 12/14/2010 10:29:25 AM EST
constant cycling like that may mean the filter is clogged remove it see what happens

Member
Avatar
Bronze
Offline
  • Joined Apr 2007
  • Posts 1146
  • EE 0% (0)
USA WV, USA
Link Posted: 12/14/2010 10:53:17 AM EST
I will check that also but I just bough a new pleated filter for it a few months ago. The house has been under some construction and alot of drywall dust in the air may have clogged it.

I will post tomorrow and let you guys know what the status is.

Thanks again for the help.

Originally Posted By proto_moose:
Originally Posted By powdershots:
if gas forced air it is mostlikely triping off on a highlimit temp sensor ,try finding intake airfilters and replace to insure good airflow,also the antisipator setting on the digital t stat might need to be changed for a highgher run time,also a heat vent might be too close to the t stat heating it up before the house, so close that one down, good luck


Did you check your filter? powdershots might be close on the limit idea.


"Those who would give up liberty for the sake of security deserve neither liberty nor security."
Basic
Offline
  • Joined Jul 2007
  • Posts 1696
  • EE 0% (0)
USA OR, USA
Link Posted: 12/14/2010 11:13:05 AM EST
Does your stat have a "Fan" setting? leave the fan running constantly.
Chances are no furnace will keep a house warm 100% of the time.
They are just not sized that large typically.

Check for any outside air or ventilation air from your unheated basement, note where it is set and then close the damper.
Re-open in in spring.

A gas furnace "Should" put out 120 F air on full heat, but that doesn't mean your house will stay 70 in the dead of winter.
It could be a problem with the furnace, so call the landlord and schedule a HVAC service call.

JIP
Team Member
Avatar
Bronze
Offline
  • Joined Sep 2008
  • Posts 5126
  • EE 0% (0)
USA PA, USA
Link Posted: 12/14/2010 12:13:54 PM EST

Originally Posted By grafixghost:
I will check that also but I just bough a new pleated filter for it a few months ago. The house has been under some construction and alot of drywall dust in the air may have clogged it.

I will post tomorrow and let you guys know what the status is.

Thanks again for the help.

Originally Posted By proto_moose:
Originally Posted By powdershots:
if gas forced air it is mostlikely triping off on a highlimit temp sensor ,try finding intake airfilters and replace to insure good airflow,also the antisipator setting on the digital t stat might need to be changed for a highgher run time,also a heat vent might be too close to the t stat heating it up before the house, so close that one down, good luck


Did you check your filter? powdershots might be close on the limit idea.



A "Few months is NOT a long time for a furnace filter especially if you are in a dusty environment. You definately want to go ahead and change that filter.