Yeah I'm trying to avoid turning off the whole main-sub-panel to do a breaker switch but it's looking like that's going to happen.
I can just install two 15A single pole breakers in place of the 30 and feed each of them with the red/black in the current run so I'm just going to do that so I have two 15A going to the outside for compressor-driven items like ice makers and beer fridges.
View Quote View All Quotes
View All Quotes
Quote History Quoted:
Yeah I'm trying to avoid turning off the whole main-sub-panel to do a breaker switch but it's looking like that's going to happen.
I can just install two 15A single pole breakers in place of the 30 and feed each of them with the red/black in the current run so I'm just going to do that so I have two 15A going to the outside for compressor-driven items like ice makers and beer fridges.
You can, as in they will fit just fine, but you shouldn't and it's against code unless you install a breaker handle tie. It is a safety issue because with single-pole breakers, you could leave one leg of the multi-wire branch circuit hot and electrocute yourself when working in the box that contains the first splice off of the 10-3 cable.
What do you mean main-sub-panel? Is it the main disconnect panel, or is it a sub-panel?
Why do you need to turn the panel off to swap breakers?
It sounds like you want a multi-wire branch circuit. That is what you're describing by using the red and the black on separate breakers for 120V instead of 240V. In that case, code requires that both breaker simultaneously disconnect, which in almost all cases will be a two-pole breaker.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductorsof a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.
(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
(D) Grouping. The ungrounded and grounded circuit conductors of each multiwire branch circuit shall be grouped in accordance with 200.4(B).
Here is what I would do:
Replace the 30A two-pole breaker with a 20A two-pole breaker.
Use 12-2 w/ ground to feed the 2 new circuits.
Of course, you could do it with a 15A two-pole breaker and 14-2, but if you can I'd go 20A.