Had the same problem with our water heater about a year ago, just over a year after we installed it new. Finally tried wiping the air intake vent holes on the bottom, stayed lit for a year. Then it went out again, so I wiped the underside, and it has stayed lit since. That was about a month ago.
View Quote View All Quotes
View All Quotes
Quote History Quoted:
Quoted:
I had a similar problem and vaccum under and inside the was always the answer.
Had the same problem with our water heater about a year ago, just over a year after we installed it new. Finally tried wiping the air intake vent holes on the bottom, stayed lit for a year. Then it went out again, so I wiped the underside, and it has stayed lit since. That was about a month ago.
Rust forms from the moisture running up the vent (and baffles) through the middle of the typical tank.
It falls down on the burner.
The gas pressure is not high enough to blow it off at that point.
It can block enough tiny orifices to both put out the pilot, block the secondary flame, or not allow it to ignite the larger burner.
The gas valve will only allow a short period with the 'flame proving' of the capillary tube heating before shutting down.
The tiny pilot fist igniters the 'flame proving' orifice (you will see the pilot more than double in size) and only then is the main burner provided with gas.