Quote History Quoted:
Current has everything to do with the breaker and wire size. The breaker should be as close to the full load amps as possible and still handle the startup. Wire is sized at 125% (article 430.22) of the full load amps, not 120%. I'm not sure what FLR means as mentioned by someone else. Should be FLA. If not subject to damage, run romex. Faster and cheaper.
View Quote
Try reading the rest of the article.
FLR means Full Load Rating and comes from the table in 430 based only on horsepower.
FLA is motor label BS that means NOTHING and is not used.
PVC is not allowed if subject to even moderate damage.
Read the Code section for rigid non-metallic conduit.
EMT is not all that tough either.
AC is even lower.
The NM rules apply to AC for protection.
Read the separate articles. Many cross back to the NM article for physical protection.
The breaker is allowed to be as large as required for start up.
There is no requirement it be "as close to the full load amps as possible."
You can get and idea of what a starting surge will be using the kV-A locked rotor code on the motor and the horsepower.
Startup is a 'locked rotor' condition. Nothing is turning yet.
The kV-A locked rotor letter to number table is in Article 430.
Motors have thermal overload built in and cannot overload wires sized correctly.
All the breaker is for is feeder protection to the motor against short circuits in the feeder.