im familiar with a lot of wiring, I plan on rewiring the garage, it has a singe 110v circiut now, a couple switches to lights and 2 outlets, all on 1 swithc in the house


I want to run 220v out there to a small sub panel
220v outlet for future use(60/80 gallon air compressor and maybe a welder, these seem to be rated at ~20A and 30A respectively)
a couple 20A circuits with a couple outlets(probably about 4-5 duplex outlets on each circuit)
2 switched 15A circuits for lights

I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?
for that run it looks like it provides for a 50A load ?  
so I am looking at a 50A breaker in the house?

also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?
Link Posted: 3/27/2015 10:23:04 PM EDT
[#1]
How big is the panel in the house and what kind of load does it currently have?
Link Posted: 3/27/2015 10:25:36 PM EDT
[#2]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
How big is the panel in the house and what kind of load does it currently have?
View Quote

I'm at work now, I'll get that info when i have time
Link Posted: 3/27/2015 11:35:52 PM EDT
[#3]
Quoted:
I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors
View Quote

18" minimum depth for the NM conduit.  use an online "conduit fill calculator" to find the correct conduit size.

Quoted:
the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?
View Quote

THWN is needed since buried conduit is classed as a wet location.
for 50A, you can use qty 3 #8 THWN's (L1, L2, N) and 1 #10 THWN for ground.

Quoted:
for that run it looks like it provides for a 50A load ?  
so I am looking at a 50A breaker in the house?
View Quote

yes, that would provide 50A of split phase 240Vac.

Quoted:
also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?
View Quote

4 wires: L1, L2, N, GND.   you also need qty 2 ground rods at the garage.

ar-jedi

Link Posted: 3/28/2015 11:51:07 AM EDT
[#4]
Quoted:
im familiar with a lot of wiring, I plan on rewiring the garage, it has a singe 110v circiut now, a couple switches to lights and 2 outlets, all on 1 swithc in the house


I want to run 220v out there to a small sub panel
220v outlet for future use(60/80 gallon air compressor and maybe a welder, these seem to be rated at ~20A and 30A respectively)
a couple 20A circuits with a couple outlets(probably about 4-5 duplex outlets on each circuit)
2 switched 15A circuits for lights

I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?
for that run it looks like it provides for a 50A load ?  
so I am looking at a 50A breaker in the house?

also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?
View Quote



Is the Garage attach to the house or is it separate from the house. If it is not attach to the house you will need to drive a ground rod at the garage also don't forget that subpanels must be 4 wire (2 hot's 1 neutral, and a ground)
Link Posted: 3/28/2015 11:56:20 AM EDT
[#5]
Discussion ForumsJump to Quoted PostQuote History
Quoted:

18" minimum depth for the NM conduit.  use an online "conduit fill calculator" to find the correct conduit size.


THWN is needed since buried conduit is classed as a wet location.
for 50A, you can use qty 3 #8 THWN's (L1, L2, N) and 1 #10 THWN for ground.


yes, that would provide 50A of split phase 240Vac.


4 wires: L1, L2, N, GND.   you also need qty 2 ground rods at the garage.

ar-jedi

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

18" minimum depth for the NM conduit.  use an online "conduit fill calculator" to find the correct conduit size.

Quoted:
the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?

THWN is needed since buried conduit is classed as a wet location.
for 50A, you can use qty 3 #8 THWN's (L1, L2, N) and 1 #10 THWN for ground.

Quoted:
for that run it looks like it provides for a 50A load ?  
so I am looking at a 50A breaker in the house?

yes, that would provide 50A of split phase 240Vac.

Quoted:
also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?

4 wires: L1, L2, N, GND.   you also need qty 2 ground rods at the garage.

ar-jedi




When did #8 wire get rated for 50 amps?
Link Posted: 3/30/2015 7:39:12 PM EDT
[#6]
Discussion ForumsJump to Quoted PostQuote History
Quoted:
When did #8 wire get rated for 50 amps?
View Quote

several charts I've come across show that #8 is good for 55A, though the 50' run drops that to 50A



and to answer questions, detached garage, 100A service to the house, 6 open breaker locations in the box
Link Posted: 3/30/2015 7:40:24 PM EDT
[#7]
Discussion ForumsJump to Quoted PostQuote History
Quoted:

18" minimum depth for the NM conduit.  use an online "conduit fill calculator" to find the correct conduit size.


THWN is needed since buried conduit is classed as a wet location.
for 50A, you can use qty 3 #8 THWN's (L1, L2, N) and 1 #10 THWN for ground.


yes, that would provide 50A of split phase 240Vac.


4 wires: L1, L2, N, GND.   you also need qty 2 ground rods at the garage.

ar-jedi

View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Quoted:
Quoted:
I plan to dig a trench, and run the plastic conduit, and will be running the individual conductors

18" minimum depth for the NM conduit.  use an online "conduit fill calculator" to find the correct conduit size.

Quoted:
the total run is probably right around 50', so, I'm thinking 8 gauge THHN wire?

THWN is needed since buried conduit is classed as a wet location.
for 50A, you can use qty 3 #8 THWN's (L1, L2, N) and 1 #10 THWN for ground.

Quoted:
for that run it looks like it provides for a 50A load ?  
so I am looking at a 50A breaker in the house?

yes, that would provide 50A of split phase 240Vac.

Quoted:
also, do I run a hot, hot, neutral and a ground, or is a ground rod at the garage called for?

4 wires: L1, L2, N, GND.   you also need qty 2 ground rods at the garage.

ar-jedi


is there a spacing between the ground rods set by code?  anything else I need to know?
Link Posted: 3/30/2015 8:28:48 PM EDT
[#8]
Yes 6 foot  minimum if I am not mistaken.
Link Posted: 4/3/2015 9:06:49 PM EDT
[#9]
#6 for 50A. Check local code on number of ground rods. We only had to drive one when I worked in Florida and Indiana as an electrician.
Link Posted: 4/14/2015 4:21:02 PM EDT
[#10]
I am now leaning towards 2-2-4-6 MHF wire, it can be direct buried, needs to be inside conduit inside the structure, and its good up to 90A, so I would have no worries with a 50A breaker, pluss, its cheaper

and I'mm planning 2 8' grounding rods 6' apart
Close Join Our Mail List to Stay Up To Date! Win a FREE Membership!

Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!

You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.


By signing up you agree to our User Agreement. *Must have a registered ARFCOM account to win.
Top Top