like the title says my air handler is pushing out cold air. It starts up but not pushing air out hard. I can feel cold air coming out of vents thats cold though. I opened up the side and there is a small black fan about 4 inches around and maybe 2 inches deep that barrely spins when its on. WTF Gonna try to get pic up of said small fan im talking about. HELP@$@!
Link Posted: 7/12/2012 8:49:19 PM EST
model number 58dla110- - - 10122
Link Posted: 7/12/2012 8:53:49 PM EST
Link Posted: 7/12/2012 10:59:55 PM EST
Have you cleaned the filter?
Link Posted: 7/12/2012 11:28:07 PM EST
That little fan is for the furnace exhaust, not circulation air.
Link Posted: 7/13/2012 2:47:54 AM EST
[Last Edit: 7/13/2012 2:49:42 AM EST by jjc155]
Originally Posted By glorifiedG:
That little fan is for the furnace exhaust, not circulation air.


this, has nothing to do with the air that comes out of the vents.

Check the filter, check to make sure the coil (the one that cools the air) in the outflow plenum is not freezing up (from low coolant) or otherwise gunked up with crap (got a dog/cat that sheds alot?) check that the actual air circulation fan is running (should be a "Hamster wheel" style fan in the very bottom of the furnace accesible by removing the lower front panel). Those are the three things that I would saw are likely.

J-

Link Posted: 7/13/2012 3:03:33 AM EST
Link Posted: 7/13/2012 3:49:35 AM EST
Originally Posted By ZW17:
Originally Posted By glacierheat34:
I opened up the side and there is a small black fan about 4 inches around and maybe 2 inches deep that barrely spins when its on.


This part has me slightly concerned.

That little fan is the combustion fan. It should not be spinning at all when calling for cooling, it's a heat only fan.

If its spinning when your indoor blower is running you could possibly have a large crack in your heat exchanger. You need to have this checked by a professional.

As for your cooling issues and lack of airflow.

Plugged filter = low air flow = iced up coil
Plugged coil = low air flow = iced up coil
Low on refrigerant = iced up coil = low air flow
Failed metering device = iced up coil = low air flow
Restriction in the refrigerant system = iced coil = low air flow

Look for the iced up indoor coil after 1hr of run time, check your filter, if clean call a pro in to repair.

Get that heat exchanger looked at ASAP.




Quoted for OP's safety.

READ THIS AGAIN!!!! Cracked heat exchanger means Carbon Monoxide.