like the title says my air handler is pushing out cold air. It starts up but not pushing air out hard. I can feel cold air coming out of vents thats cold though. I opened up the side and there is a small black fan about 4 inches around and maybe 2 inches deep that barrely spins when its on. WTF Gonna try to get pic up of said small fan im talking about. HELP@$@!
glacierheat34
Offline
Posts: 246
Feedback: 0% (0)
Link To This Post
Posted: 7/13/2012 1:49:19 AM
model number 58dla110- - - 10122
glacierheat34
Offline
Posts: 247
Feedback: 0% (0)
Link To This Post
Posted: 7/13/2012 1:53:49 AM
shrikefan
Member
Offline
Posts: 10679
Feedback: 100% (119)
Link To This Post
Posted: 7/13/2012 3:59:55 AM
Have you cleaned the filter?
Proud Member of Team Ranstad...The Fantastic Bastards

Never underestimate the power of stupid people in large groups. Circa 11/08 :(

Would cockroach semen make a good gun lube?
glorifiedG
Member
Offline
Posts: 4729
Feedback: 100% (1)
Link To This Post
Posted: 7/13/2012 4:28:07 AM
That little fan is for the furnace exhaust, not circulation air.
The Ugly truth just loves to get in the way, it's Ugly
jjc155
NRA Life Member, Oathkeeper
Offline
Posts: 6872
Feedback: 0% (0)
Link To This Post
Posted: 7/13/2012 7:47:54 AM
[Last Edit: 7/13/2012 7:49:42 AM by jjc155]
Originally Posted By glorifiedG:
That little fan is for the furnace exhaust, not circulation air.


this, has nothing to do with the air that comes out of the vents.

Check the filter, check to make sure the coil (the one that cools the air) in the outflow plenum is not freezing up (from low coolant) or otherwise gunked up with crap (got a dog/cat that sheds alot?) check that the actual air circulation fan is running (should be a "Hamster wheel" style fan in the very bottom of the furnace accesible by removing the lower front panel). Those are the three things that I would saw are likely.

J-

" I swear by my life and my love of it, that I will never live for the sake of another man, nor ask another man to live for mine." John Galt.
ZW17
O-H-I-O
Online
Posts: 17358
Feedback: 100% (32)
Link To This Post
Posted: 7/13/2012 8:03:33 AM
Originally Posted By glacierheat34:
I opened up the side and there is a small black fan about 4 inches around and maybe 2 inches deep that barrely spins when its on.


This part has me slightly concerned.

That little fan is the combustion fan. It should not be spinning at all when calling for cooling, it's a heat only fan.

If its spinning when your indoor blower is running you could possibly have a large crack in your heat exchanger. You need to have this checked by a professional.

As for your cooling issues and lack of airflow.

Plugged filter = low air flow = iced up coil
Plugged coil = low air flow = iced up coil
Low on refrigerant = iced up coil = low air flow
Failed metering device = iced up coil = low air flow
Restriction in the refrigerant system = iced coil = low air flow

Look for the iced up indoor coil after 1hr of run time, check your filter, if clean call a pro in to repair.

Get that heat exchanger looked at ASAP.


Why do you own a fire extinguisher when you have the fire department to protect you???
Elected officals should wear uniforms like NASCAR drivers so we could identify their corporate sponsors.

proto_moose
Magnets and Thermos's--How do they work?!?
Offline
Posts: 1883
Feedback: 100% (1)
Link To This Post
Posted: 7/13/2012 8:49:35 AM
Originally Posted By ZW17:
Originally Posted By glacierheat34:
I opened up the side and there is a small black fan about 4 inches around and maybe 2 inches deep that barrely spins when its on.


This part has me slightly concerned.

That little fan is the combustion fan. It should not be spinning at all when calling for cooling, it's a heat only fan.

If its spinning when your indoor blower is running you could possibly have a large crack in your heat exchanger. You need to have this checked by a professional.

As for your cooling issues and lack of airflow.

Plugged filter = low air flow = iced up coil
Plugged coil = low air flow = iced up coil
Low on refrigerant = iced up coil = low air flow
Failed metering device = iced up coil = low air flow
Restriction in the refrigerant system = iced coil = low air flow

Look for the iced up indoor coil after 1hr of run time, check your filter, if clean call a pro in to repair.

Get that heat exchanger looked at ASAP.




Quoted for OP's safety.

READ THIS AGAIN!!!! Cracked heat exchanger means Carbon Monoxide.